How did you get around these sections of NFPA 13 02'? 12.3.1.9.1 Where solid shelving in single-, double-, and multiple-row racks exceeds 20 ft2 but does not exceed 64 ft2 in area, sprinklers shall not be required below every shelf, but shall be installed at the ceiling and below shelves at intermediate levels not more than 6 ft (2 m) apart vertically. (See Section C.11.)
12.3.1.9.2 Where solid shelving in single-, double-, and multiple-row racks exceeds 64 ft2 in area or where the levels of storage exceed 6 ft (2 m), sprinklers shall be installed at the ceiling and below each level of shelving. This falls within the first one. Joe Burtell, SET, CFPS Burtell Fire Protection, Inc. [EMAIL PROTECTED] www.burtellfire.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Bill Minkel Sent: Thursday, February 28, 2008 12:53 PM To: [email protected] Subject: RE: Kohl's I did four Kohls in Nashville, TN a few years ago & no in-rack sprinklers were used to my recollection. My recall is the .45/2000 you mention with a K-25 or something similar upright storage sprinkler? Bill Minkel, Designer Western States Fire Protection, Dallas NFPA Member #2578666 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Joe Burtell Sent: Thursday, February 28, 2008 1:43 PM To: [email protected] Subject: Kohl's Has anyone done a Kohl's store lately? In particular I am interested what was done in the storage room. I asked some questions about the storage and I get the usual, we've never done that before response. Here is what they have: 17' to deck 15' of storage, 2' wide solid shelf racks, they are really shelf storage but it over the 30" limit due to back to back configuration Class I-V and Group A plastics Cartoned, unexpanded I let them know that due to the solid shelf they will need 1 level of in-rack sprinklers. They gave a .45/2000 which works fine without solid shelves. Any opinions? Joe Burtell, SET, CFPS Burtell Fire Protection, Inc. [EMAIL PROTECTED] www.burtellfire.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)