We bid it as they showed the density .45/2000 but now we have the job and it should be every designers job to verify the density's if it's strictly per NFPA or FM. Anything beyond and I agree, I'm not an engineer either. With what I know the code clearly shows 1 level of in-racks are required, so no one has showed I'm wrong so it's time for an RFI and see what the engineer and AHJ think.
Joe Burtell, SET, CFPS Burtell Fire Protection, Inc. [EMAIL PROTECTED] www.burtellfire.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Bill Minkel Sent: Thursday, February 28, 2008 1:38 PM To: [email protected] Subject: RE: Kohl's Kohl's had a detailed spec and the sprinkler protection was per their Engineer of Record & possibly insurance carrier. We were Sprinkler Contractors, not Engineers so our procedure was to design to their specs and adjust if any of the local AHJ's objected as I recall. We did not suggest to them alternatives since we were not consultants and they did not ask our advice, we were subs to the general contractor. Also Nashville at that time was still under 13-1996 I think? If Kohl's showed In-racks we installed them, my recollection however is that we had upright storage sprinklers only. Heck of a demand as I recall I even had to run some 8" main in one because of that, with 1 1/4" armovers to boot in the main store area. If you are doing the work then bid it as you see it. Bill Minkel, Designer Western States Fire Protection, Dallas NFPA Member #2578666 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Joe Burtell Sent: Thursday, February 28, 2008 2:11 PM To: [email protected] Subject: RE: Kohl's How did you get around these sections of NFPA 13 02'? 12.3.1.9.1 Where solid shelving in single-, double-, and multiple-row racks exceeds 20 ft2 but does not exceed 64 ft2 in area, sprinklers shall not be required below every shelf, but shall be installed at the ceiling and below shelves at intermediate levels not more than 6 ft (2 m) apart vertically. (See Section C.11.) 12.3.1.9.2 Where solid shelving in single-, double-, and multiple-row racks exceeds 64 ft2 in area or where the levels of storage exceed 6 ft (2 m), sprinklers shall be installed at the ceiling and below each level of shelving. This falls within the first one. Joe Burtell, SET, CFPS Burtell Fire Protection, Inc. [EMAIL PROTECTED] www.burtellfire.com -----Original Message----- Grom: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Bill Minkel Sent: Thursday, February 28, 2008 12:53 PM To: [email protected] Subject: RE: Kohl's I did four Kohls in Nashville, TN a few years ago & no in-rack sprinklers were used to my recollection. My recall is the .45/2000 you mention with a K-25 or something similar upright storage sprinkler? Bill Minkel, Designer Western States Fire Protection, Dallas NFPA Member #2578666 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Joe Burtell Sent: Thursday, February 28, 2008 1:43 PM To: [email protected] Subject: Kohl's Has anyone done a Kohl's store lately? In particular I am interested what was done in the storage room. I asked some questions about the storage and I get the usual, we've never done that before response. Here is what they have: 17' to deck 15' of storage, 2' wide solid shelf racks, they are really shelf storage but it over the 30" limit due to back to back configuration Class I-V and Group A plastics Cartoned, unexpanded I let them know that due to the solid shelf they will need 1 level of in-rack sprinklers. They gave a .45/2000 which works fine without solid shelves. Any opinions? Joe Burtell, SET, CFPS Burtell Fire Protection, Inc. [EMAIL PROTECTED] www.burtellfire.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)