I don't believe so, since both are the function of the Dept. of Health. and the plumbing code "shall apply to the erection installation, alteration or repair of or replacement of and use or maint. of plumbing systems within the jurisdiction." (Fire Sprinkler systems are not plumbing, since you need to go to a different standard to find out how to install repair or alter them.) Additionally the Cross Connection control manual of Colo. in conjunction with the the Clean Drinking water act and several other federal and state laws say cross connection shall be the responsibility of the water purveyor, not the code official or the plumbing code official. Additionally realize that the plumbing code ends 5' outside of the foundation. In places like Ca FL and HI AZ NM and TX the backflows are located above ground and more than 5' outside of the building.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- From: "Ed Kramer" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Wednesday, February 27, 2008 9:26 AM
Subject: RE: RP BFP on ALL systems


Thom, would the locally adopted plumbing code trump the 'Colorado Cross
Connection Control Manual'?  Not that it matters for those cases where the
water purveyor elects to require an RP on everything, but it could force
them to require an RP on everything.

Ed Kramer
Littleton, CO

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:sprinklerforum-
[EMAIL PROTECTED] On Behalf Of Thom McMahon
Sent: Wednesday, February 27, 2008 8:39 AM
To: [email protected]
Subject: Re: RP BFP on ALL systems

Ed:
In Colo you are under the Dept. of health for backflow prevention,
specifically the "Colorado Cross Connection Control Manual" This places
the
requirements for cross connection control on the water purveyors, and
allows
the use of double check valve assemblies for fire protection that don't
contain additive's. The water purveyor can require all backflows for FP
to
be RPZ type, but the state does not.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: "Ed Kramer" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Wednesday, February 27, 2008 7:55 AM
Subject: RE: RP BFP on ALL systems


> Thanks, Craig.  What edition of IPC is that from?
>
> Ed Kramer
> Littleton, CO
>
>> -----Original Message-----
>> From: [EMAIL PROTECTED]
[mailto:sprinklerforum-
>> [EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED]
>> Sent: Wednesday, February 27, 2008 7:17 AM
>> To: [email protected]
>> Subject: RE: RP BFP on ALL systems
>>
>> IPC Table 608.1 refers to Double Check, Double Check detector,
Reduced
>> Pressure, Reduced Pressure Detector styles applicable to fire
>> protection.  Take your pick, but check with the water purveyor first
as
>> they may have specific requirements that nail it down.
>>
>> 608.16.4 Says sprinkler systems are to use double-check valve
assembly
>> or reduced pressure.  Also some interesting exceptions for deluge,
>> preaction or dry systems.
>>
>> RP's are the standard for chemical additive systems like antifreeze.
>>
>>
>> Craig L. Prahl, CET
>> Fire Protection Group
>> Mechanical Department
>> CH2MHILL
>> Lockwood Greene
>> 1500 International Drive
>> PO Box 491, Spartanburg, SC  29304-0491
>> Direct - 864.599.4102
>> Fax - 864.599.8439
>> [EMAIL PROTECTED]
>> http://www.lg.com
>>
>>
>> -----Original Message-----
>> From: [EMAIL PROTECTED]
>> [mailto:[EMAIL PROTECTED] On Behalf Of Ed
Kramer
>> Sent: Tuesday, February 26, 2008 9:39 PM
>> To: [email protected]
>> Subject: RP BFP on ALL systems
>>
>> John, thanks for that tidbit.  We have a few jurisdictions in this
area
>> that require the RP on all systems, but most don't.  Being a
sprinkler
>> guy, I really don't pay much attention to what edition of what
plumbing
>> code is being enforced.  I guess I need to rethink that.  Can anyone
>> clue me in on what the International Plumbing Code says concerning
>> BFP's?
>>
>> Ed Kramer
>> Littleton, CO
>>
>>
>> > The 2006 National Standard Plumbing Code provides the requirement
for
>> > RPZ when antifreeze is present (type not stipulated) or an FDC is
>> > present (the 1700ft distance to non potable source has been
>> > eliminated) on a water based fire protection system.
>> >
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email
>> to:[EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email to:Sprinklerforum-
>> [EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to