Thanks, Craig.  What edition of IPC is that from?

Ed Kramer
Littleton, CO

> -----Original Message-----
> From: [EMAIL PROTECTED] [mailto:sprinklerforum-
> [EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED]
> Sent: Wednesday, February 27, 2008 7:17 AM
> To: [email protected]
> Subject: RE: RP BFP on ALL systems
> 
> IPC Table 608.1 refers to Double Check, Double Check detector, Reduced
> Pressure, Reduced Pressure Detector styles applicable to fire
> protection.  Take your pick, but check with the water purveyor first as
> they may have specific requirements that nail it down.
> 
> 608.16.4 Says sprinkler systems are to use double-check valve assembly
> or reduced pressure.  Also some interesting exceptions for deluge,
> preaction or dry systems.
> 
> RP's are the standard for chemical additive systems like antifreeze.
> 
> 
> Craig L. Prahl, CET
> Fire Protection Group
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [EMAIL PROTECTED]
> http://www.lg.com
> 
> 
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Ed Kramer
> Sent: Tuesday, February 26, 2008 9:39 PM
> To: [email protected]
> Subject: RP BFP on ALL systems
> 
> John, thanks for that tidbit.  We have a few jurisdictions in this area
> that require the RP on all systems, but most don't.  Being a sprinkler
> guy, I really don't pay much attention to what edition of what plumbing
> code is being enforced.  I guess I need to rethink that.  Can anyone
> clue me in on what the International Plumbing Code says concerning
> BFP's?
> 
> Ed Kramer
> Littleton, CO
> 
> 
> > The 2006 National Standard Plumbing Code provides the requirement for
> > RPZ when antifreeze is present (type not stipulated) or an FDC is
> > present (the 1700ft distance to non potable source has been
> > eliminated) on a water based fire protection system.
> >
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email to:Sprinklerforum-
> [EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to