Yeah but not all 2 hr fire walls, double doors in corridors with magnetic
holders are horizontal exits.  Don't be confused.  They are rarely used in
my experience. Ask your architect.  Generally, they are for very long travel
distances and a short cut around putting in another exit stair.  Think
really massive complexes where you go from one building to another.  But
that's a generalization too and not to be trusted. Ask your architect.     

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [EMAIL PROTECTED]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jamie Seidl
Sent: Friday, March 07, 2008 3:07 PM
To: [email protected]
Subject: RE: Horizontal Exits

Chap 10 of the 2003 IBC.
Exit, Horizontal.  A path of egress travel from one building to an area in
another building on approximately the same level, or a path of egress travel
through or around a wall or partition to an area on approximately the same
level in the same building, which affords safety from fire and smoke from
the area of incidence and areas communicating therewith.

(Think 2 hr fire walls, double doors in corridors with magnetic holders).

Jamie Seidl

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Richard
Battershell
Sent: Friday, March 07, 2008 3:45 PM
To: [email protected]
Subject: Horizontal Exits


Class I standpipes as per NFPA 14 7.3.2 (2)2004 ed. requires hose
connections be provided "On each side of the wall adjacent to the exit
openings of horizontal exits".  What constitutes a horizontal exit?

Thanks for the help.


Richard Battershell





_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to