How does the group feel on the occupancy classification of a rated room in a 
building that contains a 275 Gal #2 Fuel tank for the rooftop generator?  The 
room is on the ground level and the tank is 130 feet above on the roof.
   
  The architect is calling this a OH2 hazard and protecting the room with a 
single K5.6 QR Head @ .18 over 1500 Ft2.  His reasoning is that the tank is not 
combustible, just the product in it .......  Im leaning towards a EH 
designation in the event of fire the fuel would be more than capable of 
supporting combustion.  At the very least I dont see the current configuration 
as being adequate.
   
  Thanks,
   
  Dave P.
  An AHJ in NJ