I would agree with OH2 (or even OH1).  It is a combustible liquid in a
closed system.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of David
Phelan
Sent: Monday, March 10, 2008 1:51 PM
To: [email protected]
Subject: Fuel Tank Rooms

How does the group feel on the occupancy classification of a rated room
in a building that contains a 275 Gal #2 Fuel tank for the rooftop
generator?  The room is on the ground level and the tank is 130 feet
above on the roof.
   
  The architect is calling this a OH2 hazard and protecting the room
with a single K5.6 QR Head @ .18 over 1500 Ft2.  His reasoning is that
the tank is not combustible, just the product in it .......  Im leaning
towards a EH designation in the event of fire the fuel would be more
than capable of supporting combustion.  At the very least I dont see the
current configuration as being adequate.
   
  Thanks,
   
  Dave P.
  An AHJ in NJ