Roland,
Chapter 5, General Building Heights and Areas, of the IBC-2006 is where I
was looking to try and answer the original post. However, the original
post does not specify the occupancy (R1, R2, or what?) or the building
arrangement, shape, frontage that might allow an area increase, not does it
call out what code is being used.
If using IBC you can have a wood building with no protection and the code
allows a 2 story, 7000 square foot building. If you sprinkler it you can
have a 3 story 21,000 square foot building. If there is frontage available
this square footage increases, maybe even close to the 30,000 square feet
that exists. But the post said a 4 story building which requires the
construction to be a sprinklered Type V-A construction. That being the
case you can build a 4 story 36,000 square foot building.
But lets say you have a building that has too much square footage to meet
the building code limits. In that case you have to build a fire wall.
This is one that goes all the way up through the building and through the
roof and that stays in place if the other side burns down. This creates
two buildings, not one building with a partition. The IBC allows no
penetrations of this type of wall so with the door in the corridor through
the wall it (they) do not meet the definition of party walls per IBC.
The construction of this type of wall does not allow the increase of a
building's square footage. It creates two separate buildings. You are
right. The A&E needs to be contacted to answer the purpose of the walls.
Plus, the original question was about zoning due to compartmentation.
On zoning, the IFC (section 907.9) calls out a maximum size of 22,500
square feet for a zone, but generally it is allowed to match the size of a
single sprinkler system. It is possible the local codes and AHJ may not
permit increasing the size of the fire alarm zone.
John Hoffman, P.E.
Fire Protection Engineer
Facility Engineering Services, KCP, LLC
2000 E. 95th Street
Kansas City, MO 64131
Ph: 816-997-7213
Roland Huggins
<[EMAIL PROTECTED]
inkler.org> To
Sent by: [email protected]
sprinklerforum-bo cc
[EMAIL PROTECTED]
er.org Subject
Re: Horizontal Exits Part 88
03/11/2008 01:42
PM
Please respond to
[EMAIL PROTECTED]
resprinkler.org
Since the building code is not my claim to fame, I am expressing
OPINIONS just like any other FPE.
Having said that, JOHN, what is your read on whether Chap 5 allows
barriers to be used to increase the floor area for a single building?
502.1 seems rather explicit (and it complies with the underlying
philosophy) that it's bounded by either exterior walls or fire
walls. Just because another chapter mentions barriers dividing the
area of a floor, that's for a different purpose (such as overall
exposed area that triggers sprinklers as in chap 9). Location has
meaning as mentioned on the fire alarm impacting sprinkler zoning
misconception.
This will be my last message on this topic since we've beaten this
thing to death. There is a moral to this thread. Be careful when
you casual accept providing code guidance just because the owner
doesn't want to hire an engineer or the architect doesn't realize
they know nothing about fire protection.
Roland
On Mar 11, 2008, at 10:54 AM, John Drucker wrote:
>
> While that may be true, providing a firewall where a fire separation
> assembly will do is unusual. The question needs to be asked of the
> architect as to the purpose of same, i.e., fire areas or separate
> buildings. The truth is in the answer which will be memorialized. The
> end result will be when the owner tries to sell the building or
> building(s).
>
> John Drucker
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)