Roland wrote; Having said that, JOHN, what is your read on whether Chap 5
allows  
barriers to be used to increase the floor area for a single building?

If you mean Fire "Barriers" or Fire Partitions, NO !

2006 IBC 506.1 addresses Area Modifications. The commentary says it all;
"Besides increasing the fire resistance (utilizing a higher construction
type) of the building structure, in general there are TWO circumstances that
would decrease a buildings fire hazard. These are:

1) Isolating the building from other structures 2) Equipping it with a fire
suppression system"  

Number 2) is a no brainer. Lets look at # 1, Isolation. Just how is this
accomplished ?

a) 506.2 Frontage Increase - Frontage on streets, or open spaces adjoining
or having access to the public way.  This gives the fire service access to
the building and limits exposure to other buildings on the side(s) taken as
"open frontage" credit.  Remember the starting point for open frontage
credit is "where a building has more then 25% of its perimeter on a public
way or open space having a width of 20 feet", the first 25% is a given, thus
the maximum credit for open frontage is 75%.  

If=[F/P]-0.25](W/30)

Thats it. No mention in the code of fire barriers providing area increase
benefits. Sure a firewall (705.1) or party wall (705.1.1) will help because
each structure gets treated as a separate building when using Table 503, but
not if the designer intents to use them as fire barriers or partitions, i.e.
openings and penetrations. If one uses a firewall or party wall they must do
so in compliance with 705.1/705.1.1 and not 706/708. Designers simply cant
mix and match since the intent of the fire separation interacts with other
provisions of the code.

I think the fire area provisions of Chapter 9 get confused with the area
provisions. They are different. Before we get to Chapter 9 one needs to get
past Chapter 5. And remember if a Chapter 5 area increase was accomplished
with sprinklers one can't squash the sprinklers by chopping a building up
using fire areas pursuant to Chapter 9.

Lastly be careful of area increases and double dipping. 2006 IBC Table
601/602 note e. has been known to wreck many an architects day. The moral to
note e., dont get greedy !.

PS- With sprinklers fetching 300% (single story) and 200% (multiple story)
area increase "incentives" concurrent with height increase the sprinkler
"option" is winking at you. 

John Drucker
Fire Protection Subcode Official (AHJ)
New Jersey


 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Tuesday, March 11, 2008 2:42 PM
To: [email protected]
Subject: Re: Horizontal Exits Part 88

Since the building code is not my claim to fame, I am expressing  
OPINIONS just like any other FPE.

Having said that, JOHN, what is your read on whether Chap 5 allows  
barriers to be used to increase the floor area for a single building?

502.1 seems rather explicit (and it complies with the underlying  
philosophy) that it's bounded by either exterior walls or fire   
walls.  Just because another chapter mentions barriers dividing the  
area of a floor, that's for a different purpose (such as overall  
exposed area that triggers sprinklers as in chap 9).   Location has  
meaning as mentioned on the fire alarm impacting sprinkler zoning  
misconception.

This will be my last message on this topic since we've beaten this  
thing to death.  There is a moral to this thread.  Be careful when  
you casual accept providing code guidance just because the owner  
doesn't want to hire an engineer or the architect doesn't realize  
they know nothing about fire protection.

Roland

On Mar 11, 2008, at 10:54 AM, John Drucker wrote:

>
> While that may be true, providing a firewall where a fire separation
> assembly will do is unusual.  The question needs to be asked of the
> architect as to the purpose of same, i.e., fire areas or separate
> buildings. The truth is in the answer which will be memorialized. The
> end result will be when the owner tries to sell the building or
> building(s).
>
> John Drucker

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to