it will throw wider but the activation side must be accounted for. The wall that captures and turns the heat is the wall that it is installed in. That wall is only 6 inches wide. This is no different than installing a pendent sprinkler beneath a soffit. IT is assigned the floor area directly beneath the soffit but NOT any of the floor beyond the soffit edge (although water will flow there). AS stated in 8.6.4.1.1.1, the distance to the ceiling is measured throughout the assigned area of coverage (which is an activation issue).

Roland

On Apr 3, 2008, at 4:09 AM, Dewayne Martinez wrote:

Roland, if I understand you correctly, because that head is installed on a wall 6 inches wide wall it will only correctly throw a path 16ft long
by 6in wide (for 16'x16' sprinkler)? Why?
Thanks,
Dewayne

-----Original Message-----

_______________________________________________