it will throw wider but the activation side must be accounted for.
The wall that captures and turns the heat is the wall that it is
installed in. That wall is only 6 inches wide. This is no different
than installing a pendent sprinkler beneath a soffit. IT is assigned
the floor area directly beneath the soffit but NOT any of the floor
beyond the soffit edge (although water will flow there). AS stated
in 8.6.4.1.1.1, the distance to the ceiling is measured throughout
the assigned area of coverage (which is an activation issue).
Roland
On Apr 3, 2008, at 4:09 AM, Dewayne Martinez wrote:
Roland, if I understand you correctly, because that head is
installed on
a wall 6 inches wide wall it will only correctly throw a path 16ft
long
by 6in wide (for 16'x16' sprinkler)? Why?
Thanks,
Dewayne