Are you neglecting the thickness of the ceiling jet? I certainly agree
there are a lot of variables that go into the question if and when the head
will operate. Relying on any one might be oversimplifying the question. To
say the wall is so integral might be a stretch. If so why do warehouse
heads operate? Or better what if the throw he is trying to cover is 10'.
Would there be a question about putting an ECBUP at 12" below the clg?
Dynamics would be the same in getting the head to operate. Probably look
awful. But isn't this why we plan on more than one head operating and
usually one or two go off.
What wasn't said in the first email was an assumption there are other heads
that cover the remaining floor space. Of course then the question is, is
there problems with heads inside the protection area of other heads? That's
what I run into when thinking about these atypical locations.
And the head under the soffit is assigned floor area if the soffit is <3'
down from the ceiling. I know until the change for steps in clg. you had a
point.
Final point if what you said is true there are like a gazillion apartment
buildings that are deficient. Your argument would not be much different
than putting the head on the corner of a 90 deg. wall but only counting the
floor coverage of the wall the head is on and not the open air to the other
side.
Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
763-658-4483
763-658-4921 fax
Email: [EMAIL PROTECTED]
Mail: P.O. Box 69
Waverly, MN 55390
Location: 4439 Hwy 12 SW
Waverly, MN 55390
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Thursday, April 03, 2008 10:28 AM
To: [email protected]
Subject: Re: sidewalls on the end wall
it will throw wider but the activation side must be accounted for.
The wall that captures and turns the heat is the wall that it is
installed in. That wall is only 6 inches wide. This is no different
than installing a pendent sprinkler beneath a soffit. IT is assigned
the floor area directly beneath the soffit but NOT any of the floor
beyond the soffit edge (although water will flow there). AS stated
in 8.6.4.1.1.1, the distance to the ceiling is measured throughout
the assigned area of coverage (which is an activation issue).
Roland
On Apr 3, 2008, at 4:09 AM, Dewayne Martinez wrote:
> Roland, if I understand you correctly, because that head is
> installed on
> a wall 6 inches wide wall it will only correctly throw a path 16ft
> long
> by 6in wide (for 16'x16' sprinkler)? Why?
> Thanks,
> Dewayne
>
> -----Original Message-----
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)