Jose,
Sprinklers: no, there is not.
Hi-expansion foam: maybe, if the AHJ accepts it.
Inert gas or CO2: maybe, but then you will have at least nozzles
along the walls at different levels in addition to the ceiling nozzles.
I never met a customer who wants in-rack sprinklers.
But when we show the cost estimate of other possible solutions with
storage over 12,2 m high, they usually choose in-rack sprinklers voluntarily.
Maybe the AHJ will accept ceiling sprinklers only if the customer
stores non-combustible materials (like rocks on metal pallets).
What commodity does your client store?
Other common option:
Decrease the storage to 12,2 m and install a suspended ceiling at 13,7 m.
Yours sincerely,
Frans Stoop
TOS architecture & fire protection
Netherlands <[EMAIL PROTECTED]>
------------------disclaimer------------------
Senders and recipients of e-mail should be aware of the fact that an
e-mail message can never be confidential. On its way between sender
and recipient each e-mail message is stored and transfered by
averagely 5 or 6 servers, each of which can be located anywhere in
the world. Some servers keep the e-mail correspondence on storage for
a short time only, other servers may store the communication for many
years. In some countries the authorities filter all e-mail
correspondence that passes by and may decide to read the content.
Also, the operators of e-mail servers have easy access to the e-mail
messages that pass by.
------------------disclaimer------------------
At 10:39 13-4-2008 -0400, Jose Prada wrote:
Dear Sirs:
I always read all your smart comments. I have a situation with a 17
mts celing high warehouse with 15 mts high multiple raw rack storage
(commodity II). The customer does not want to use sprinkler in rack. I
thougth about using ESFR sprinkler but high limit is 13.7mts. My
question is, is there a "only celing protection" solution for this
issue?
Regards,
Jose Prada
SISPROFUEGO, C.A.
Venezuela