There are just some cases where in-rack sprinklers can not be avoided. NEVER use CO2 in an occupied or potentially occupied space. And gaseous is great for small rooms but for large warehouse rooms it is very impractical and in most cases just wouldn't work.
Ceiling sprinklers with in-racks are your best and simplest option. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of SISPROFUEGO, C.A. - José Prada Sent: Sunday, April 13, 2008 10:40 AM To: [email protected] Subject: High Storage / High Celing Dear Sirs: I always read all your smart comments. I have a situation with a 17 mts celing high warehouse with 15 mts high multiple raw rack storage (commodity II). The customer does not want to use sprinkler in rack. I thougth about using ESFR sprinkler but high limit is 13.7mts. My quuestion is, is there a "only celing protection" solution for this issue? Regards, Jose Prada SISPROFUEGO, C.A. Venezuela _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)