Ron, 

I think the water districts in our area all use one inch taps off the main 
regardless.  I personally haven't been on any that were changed. If it others 
in the office have had this experience I've missed it.  On the technical side, 
the 5/8 x 3/4 and 1 x 1 meter use the same main tap. Changing would not be 
difficult.

The non-tech side is the old issue of system development fees. But lets start 
another thread if we want to discuss that.

Yours,

Bruce V.

 -------------- Original message ----------------------
From: "Ron Greenman" <[EMAIL PROTECTED]>
> Bruce,
> 
> Meter setters seem to be a big problem. Any experience/comments with these?
> 
> On Tue, Apr 15, 2008 at 11:06 PM,  <[EMAIL PROTECTED]> wrote:
> >
> >  Dear List,
> >
> >  Reading this stream of thought I have lost track of what the concerns are 
> with this test.  Is it the time it takes? Is it the difficulty of correcting 
> the 
> problem when the test fails?
> >
> >  We have learned a number of things by  witnessing these tests.
> >
> >  Sometimes PRV's are upstream of the "T" separating the domestic and 
> > sprinkler 
> lines.  These have caused the system to fail to be able to deliver the design 
> flow. Usually the PRV can be moved to the domestic side of the "T".
> >
> >  As was mentioned by some writers systems installed not to plans have 
> > caused 
> systems to fail to be able to deliver the design flow. This was particularly 
> acute when we used to see 3/4" cpvc installed.
> >
> >  We have seen systems fail to deliver the design flows due to undergrounds 
> > not 
> installed as the sprinkler designer showed. Of course this crosses trade 
> lines. 
> It is unclear if the sprinkler contractor has had direct contact with the 
> plumbing contractor.
> >
> >  We used to commonly see systems fail to flow the design flow due to debris 
> > in 
> the heads.  The sprinkler contractors back flushed the  systems to get debris 
> out. As a pattern was observed we talked with the building inspectors. We 
> discovered that normal plumbing supply lines, or underground from our point 
> of 
> view, are not flushed.  The observation is that material just passes through 
> plumbing fixtures.*  We now require a UG flush.  It is common to see material 
> come out of the line that would not pass a sprinkler head.
> >
> >  Yours,
> >
> >  Bruce Verhei
> >
> >
> >  * If any one out there is having a home built, I think I'd recommend a 
> > flush 
> of the plumbing supply prior to connection.  My plumbing inspectors might be 
> right about debris passing through most fixtures.  I am not so sure of the 
> fridge ice maker, or the dishwasher supply.  When I say we see debris 
> sometimes, 
> I mean we almost always see some if a trial flush hasn't been done before we 
> get 
> there.  bv
> >
> >
> >
> >
> >   -------------- Original message ----------------------
> >  From: "Matthew J. Willis" <[EMAIL PROTECTED]>
> >  > I think it is great that some of the best sprinkler minds in the world, 
> with
> >  > access to the latest technology, can have such an informative and 
> > elaborate
> >  > discussion over a 5 gallon bucket. We do require this type of test on
> >  > another system... Do we not do partial flooding test (or full flooding if
> >  > the system isn't shut off quick enough)on our High X foam systems? As 
> > Cliff
> >  > pointed out, the pipe or walls shown on the drawings and calcs, are not
> >  > necessarily the ones that end up in the building.
> >  >
> >  > R/
> >  >
> >  > Matt
> >  >
> >  > Matthew J. Willis
> >  > Living Water Fire Protection, LLC.
> >  > 1160 McKenzie Rd.
> >  > PO Box 877
> >  > Cantonment, FL. 32533
> >  > 850-937-1850 Voice
> >  > 850-937-1852 Facsimile
> >  > [EMAIL PROTECTED]
> >  >
> >  >
> >  > ----- >-----Original Message-----
> >  > ----- >From: [EMAIL PROTECTED]
> >  > ----- >[mailto:[EMAIL PROTECTED] On
> >  > ----- >Behalf Of Chris Cahill
> >  > ----- >Sent: Tuesday, April 15, 2008 1:25 PM
> >  > ----- >To: [email protected]
> >  > ----- >Subject: RE: What is a Bucket Test? (TIA Needed)
> >  > ----- >
> >  > ----- >So the implied assumption is we will apparently by
> >  > ----- >default accept systems designed by incompetent,
> >  > ----- >untrained designers and installed by incompetent
> >  > ----- >untrained installers and approved by incompetent AHJ's?
> >  > ----- >I don't like the premise of that.  Perhaps we need a
> >  > ----- >better system to weed out the incompetence.
> >  > ----- >
> >  > ----- >But thinking more is this any different in what is
> >  > ----- >currently going on in the commercial side or large
> >  > ----- >residential side?  I'd argue adding homes will make it
> >  > ----- >no worse or better.  There are plenty of trunk slammer.
> >  > ----- >
> >  > ----- >And unless the premise is wrong (that there is an
> >  > ----- >abundance of incompetence
> >  > ----- >already) nothing in this discussion has shed light on
> >  > ----- >why not do all systems (13D, 13R and 13)?  Every
> >  > ----- >argument for tests in 13D has the same reasoning that
> >  > ----- >could be applied to any system.  How many AHJ's can tell
> >  > ----- >the difference between 1 1/2" and 2"?  I know a few can
> >  > ----- >read but at more than a few feet even that is tough.
> >  > ----- >Easy substitution and I'd bet you'd get away with it 8
> >  > ----- >out of 10 times.  Bucket test would reveal that.   And
> >  > ----- >the sad part is IMHO
> >  > ----- >13D's are the easiest to get right.  I mean the hazard
> >  > ----- >is defined, obstructions are basically not an issue, we
> >  > ----- >only sprinkler about 1/2 the rooms, no attics or trusses.
> >  > ----- >
> >  > ----- >This isn't meant to pick on you or Reliable but why do
> >  > ----- >you sell heads to incompetent companies?  Same could be
> >  > ----- >asked of all the suppliers.  You're just the lucky one
> >  > ----- >man enough to be here on a regular basis.
> >  > ----- >
> >  > ----- >I certainly can't go buy a kitchen hood system without
> >  > ----- >training from the manufactures which I presume
> >  > ----- >demonstrates competence. If you don't take offense,
> >  > ----- >again none meant, could this be an interesting
> >  > ----- >discussion point.
> >  > ----- >
> >  > ----- >Chris Cahill, P.E.
> >  > ----- >Fire Protection Engineer
> >  > ----- >Sentry Fire Protection, Inc.
> >  > ----- >
> >  > ----- >763-658-4483
> >  > ----- >763-658-4921 fax
> >  > ----- >
> >  > ----- >Email: [EMAIL PROTECTED]
> >  > ----- >
> >  > ----- >Mail: P.O. Box 69
> >  > ----- >        Waverly, MN 55390
> >  > ----- >
> >  > ----- >Location: 4439 Hwy 12 SW
> >  > ----- >              Waverly, MN 55390
> >  > ----- >-----Original Message-----
> >  > ----- >From: [EMAIL PROTECTED]
> >  > ----- >[mailto:[EMAIL PROTECTED] On
> >  > ----- >Behalf Of Mike Brown
> >  > ----- >(TECH- GVL)
> >  > ----- >Sent: Tuesday, April 15, 2008 12:18 PM
> >  > ----- >To: [email protected]
> >  > ----- >Subject: RE: What is a Bucket Test? (TIA Needed)
> >  > ----- >
> >  > ----- >John
> >  > ----- >If you are working in an environment where the projects
> >  > ----- >are designed by competent, trained designers and
> >  > ----- >installed by competent trained installers there may not
> >  > ----- >be a concern that the installation will perform the way
> >  > ----- >it is designed.  However, should residential sprinklers
> >  > ----- >be mandated the demand for design and installation will
> >  > ----- >become much greater than most of our approval agencies
> >  > ----- >and contractors will be able to handle.  The is more
> >  > ----- >true in residential situation where the market may be
> >  > ----- >flooded with "trunk slammers"
> >  > ----- >or unqualified companies doing the residential work. You
> >  > ----- >would be surprised at the number of sprinkler
> >  > ----- >contractors that had failures when Cobb County first
> >  > ----- >started requiring the "Put the Water in The Bucket".  In
> >  > ----- >many parts of the country the AHJ may know little or
> >  > ----- >nothing about hydraulics and pretty much approve what is
> >  > ----- >put in front of him.  The Fire Service will also
> >  > ----- >experience shortages of trained inspectors if installing
> >  > ----- >residential sprinkler is mandated for single family
> >  > ----- >homes.  Several large installer in GA had problems
> >  > ----- >passing the test when they were first started.
> >  > ----- >
> >  > ----- >Like Cliff, I have said my three dollars worth.  By the
> >  > ----- >way please purchase my two books from AFSA:  The
> >  > ----- >leadership Ladder", and "Estimating, Bidding, Selling
> >  > ----- >and Contracting for Fire Sprinklers."
> >  > ----- >
> >  > ----- >I need to money to retire.
> >  > ----- >
> >  > ----- >Michael L. Brown
> >  > ----- >Manager of Technical Services
> >  > ----- >The Reliable Automatic Sprinkler Company, Inc.'
> >  > ----- >[EMAIL PROTECTED]
> >  > ----- >www.reliablesprinkler.com
> >  > ----- >(864) 843-5228
> >  > ----- >
> >  > ----- >
> >  > ----- >-----Original Message-----
> >  > ----- >From: [EMAIL PROTECTED]
> >  > ----- >[mailto:[EMAIL PROTECTED] On
> >  > ----- >Behalf Of John Drucker
> >  > ----- >Sent: Tuesday, April 15, 2008 11:57 AM
> >  > ----- >To: [email protected]
> >  > ----- >Subject: RE: What is a Bucket Test? (TIA Needed)
> >  > ----- >
> >  > ----- >Thanks Mike,
> >  > ----- >
> >  > ----- >I understand the concept, however what if a) the job is
> >  > ----- >installed to plan & calcs b) the job is installed to
> >  > ----- >revised plans & calcs. ?  What I'm getting at is the
> >  > ----- >need for the bucket test if the plans and calcs
> >  > ----- >demonstrate compliance.
> >  > ----- >
> >  > ----- >
> >  > ----- >What I'm getting at is just how reliable are hydraulic
> >  > ----- >calcs  ? On the surface the bucket test implies that
> >  > ----- >hydraulic calculations in of themselves are not to be
> >  > ----- >relied on and that proof of hydraulic performance is
> >  > ----- >neccesary. If that's the case how about 13R and 13
> >  > ----- >Systems ?.   Its not a water supply "connection" issue
> >  > ----- >since a main
> >  > ----- >drain test is the accepted method to validate this.
> >  > ----- >While the bucket test also performs this function, the
> >  > ----- >need to measure performance in the area of operation
> >  > ----- >serves no other purpose then to validate hydraulic
> >  > ----- >design. If it's the installation, i.e. obstructions,
> >  > ----- >pipe size, sprinkler heads we're concerned about we need
> >  > ----- >to be flow testing beyond the area of operation.
> >  > ----- >
> >  > ----- >Lastly theres nothing in our adopted codes or standards
> >  > ----- >that require a "bucket test". Frankly a contractor would
> >  > ----- >well be within their right to appeal my decision to
> >  > ----- >require such a test.  Don't take that as I don't believe
> >  > ----- >theres some validity to "bucket tests", I do, but theres
> >  > ----- >nothing for me to hang my enforcement hat on and we all
> >  > ----- >know how contractors insist on "show me in the code."
> >  > ----- >
> >  > ----- >Sincerely,
> >  > ----- >
> >  > ----- >John Drucker
> >  > ----- >Fire Protection Subcode Official (AHJ)
> >  > ----- >New Jersey
> >  > ----- >
> >  > ----- >Safe Buildings Save Lives !
> >  > ----- >
> >  > ----- >
> >  > ----- >
> >  > ----- >-----Original Message-----
> >  > ----- >From: [EMAIL PROTECTED]
> >  > ----- >[mailto:[EMAIL PROTECTED] On
> >  > ----- >Behalf Of Mike Brown (TECH- GVL)
> >  > ----- >Sent: Tuesday, April 15, 2008 11:19 AM
> >  > ----- >To: [email protected]
> >  > ----- >Subject: RE: What is a Bucket Test? (TIA Needed)
> >  > ----- >
> >  > ----- >John
> >  > ----- >You start with a set of approved plans with the
> >  > ----- >hydraulic calculations and a permit.  There would be
> >  > ----- >various stages of inspection depending on the local fire
> >  > ----- >marshal and the "Bucket" test would be before cover up
> >  > ----- >of the pipe and fittings. If there have been changes
> >  > ----- >made to the piping,they should show up on an as-built
> >  > ----- >drawing (as-built drawings are difficult to get correct
> >  > ----- >even with commercial systems).  The bucket test would at
> >  > ----- >least insure that the remote sprinklers flow the minimum
> >  > ----- >water as per the hydraulic calculations.
> >  > ----- >
> >  > ----- >
> >  > ----- >Michael L. Brown
> >  > ----- >Manager of Technical Services
> >  > ----- >The Reliable Automatic Sprinkler Company, Inc.'
> >  > ----- >[EMAIL PROTECTED]
> >  > ----- >www.reliablesprinkler.com
> >  > ----- >(864) 843-5228
> >  > ----- >
> >  > ----- >-----Original Message-----
> >  > ----- >From: [EMAIL PROTECTED]
> >  > ----- >[mailto:[EMAIL PROTECTED] On
> >  > ----- >Behalf Of John Drucker
> >  > ----- >Sent: Monday, April 14, 2008 4:03 PM
> >  > ----- >To: [email protected]
> >  > ----- >Subject: RE: What is a Bucket Test? (TIA Needed)
> >  > ----- >
> >  > ----- >Mike,
> >  > ----- >
> >  > ----- >In addition to revised plans and hydraulic calculations
> >  > ----- >where the job wasn't installed to the original plan ?
> >  > ----- >
> >  > ----- >John Drucker
> >  > ----- >Fire Protection Subcode Official (AHJ)
> >  > ----- >New Jersey
> >  > ----- >
> >  > ----- >
> >  > ----- >-----Original Message-----
> >  > ----- >From: [EMAIL PROTECTED]
> >  > ----- >[mailto:[EMAIL PROTECTED] On
> >  > ----- >Behalf Of Mike Brown (TECH- GVL)
> >  > ----- >Sent: Monday, April 14, 2008 3:56 PM
> >  > ----- >To: [email protected]
> >  > ----- >Subject: RE: What is a Bucket Test? (TIA Needed)
> >  > ----- >
> >  > ----- >I agree with Thom in that, as we are getting closer to
> >  > ----- >mandated fire sprinklers in single family homes, the
> >  > ----- >potential for a large number of new contractors,
> >  > ----- >plumbers, and assorted others (some of whom may well be
> >  > ----- >trunk slammers) will be jumping on the bandwagon.  As I
> >  > ----- >remember when we were getting a licensing law in
> >  > ----- >Georgia, we had to exempt single family homes in order
> >  > ----- >to get any kind of law.  In some states there is still
> >  > ----- >no law at all. (New York State for example has no
> >  > ----- >licensing law.) This influx of new sprinkler installers
> >  > ----- >may not be well versed sprinkler installation.  A "Put
> >  > ----- >the Water in the Bucket" test might well be a good
> >  > ----- >control measure to protect the potential home owner as
> >  > ----- >well as protecting the image of our industry.  I would
> >  > ----- >think that a test like this might be included in the
> >  > ----- >next edition of NFPA 13D.
> >  > ----- >
> >  > ----- >At least, when I see some of the questions that I get
> >  > ----- >from some sprinkler contractors and a lot of engineers,
> >  > ----- >a field test like this could give us some degree of
> >  > ----- >quality control. That would be a good thing.
> >  > ----- >
> >  > ----- >Something to consider.
> >  > ----- >
> >  > ----- >Michael L. Brown, P.L.L.  (Peon Low Life) Manager of
> >  > ----- >Technical Services The Reliable Automatic Sprinkler
> >  > ----- >Company, Inc.'
> >  > ----- >[EMAIL PROTECTED]
> >  > ----- >www.reliablesprinkler.com
> >  > ----- >(864) 843-5228
> >  > ----- >
> >  > ----- >-----Original Message-----
> >  > ----- >From: [EMAIL PROTECTED]
> >  > ----- >[mailto:[EMAIL PROTECTED] On
> >  > ----- >Behalf Of Thom McMahon
> >  > ----- >Sent: Monday, April 14, 2008 1:39 PM
> >  > ----- >To: [email protected]
> >  > ----- >Subject: Re: What is a Bucket Test? (TIA Needed)
> >  > ----- >
> >  > ----- >This "TEST" was a conditional method when 13D was new. I
> >  > ----- >have not seen a bucket test that failed, when required,
> >  > ----- >in the last 15 years.
> >  > ----- >AHJ's are more savvy, Contractors are more cautious, and
> >  > ----- >know that the field guys will be adding ells. Some just
> >  > ----- >add extra ells in the calc's and others don't use the
> >  > ----- >full residual pressure as allowed in 13D. Maybe the
> >  > ----- >bucket test would be ok if hydraulic calc's are not
> >  > ----- >required, but is a waste of time and money for Qualified
> >  > ----- > Designers and layout Tech's, Installers, and AHJ's.
> >  > ----- >
> >  > ----- >Thom McMahon
> >  > ----- >Firetech, Inc.
> >  > ----- >2560 Copper Ridge Dr
> >  > ----- >Steamboat Springs, CO 80488-2136
> >  > ----- >Tel: 970-879-7952
> >  > ----- >Fax: 970-879-7926
> >  > ----- >----- Original Message -----
> >  > ----- >From: <[EMAIL PROTECTED]>
> >  > ----- >To: <[email protected]>
> >  > ----- >Sent: Monday, April 14, 2008 10:05 AM
> >  > ----- >Subject: RE: What is a Bucket Test? (TIA Needed)
> >  > ----- >
> >  > ----- >
> >  > ----- >> Perhaps it is time to incorporate a bucket test
> >  > ----- >requirement and test
> >  > ----- >> method into 13D prior to the widespread installation
> >  > ----- >of these systems
> >  > ----- >> based on an ICC code change.  If failures are
> >  > ----- >widespread I think this
> >  > ----- >> is important enough for a TIA if there's any chance
> >  > ----- >the ICC will
> >  > ----- >> reference a current edition of 13D.  The implications
> >  > ----- >are huge if
> >  > ----- >> large numbers of 13D systems are expected to fail after being
> >  > ----- >> engineered and installed by qualified
> >  > ----- >plumbers/sprinkler companies.
> >  > ----- >>
> >  > ----- >> Bill Brooks
> >  > ----- >>
> >  > ----- >> William N. Brooks, P.E.
> >  > ----- >> Brooks Fire Protection Engineering Inc.
> >  > ----- >> 372 Wilett Drive
> >  > ----- >> Severna Park, MD 21146
> >  > ----- >> 410-544-3620 Phone
> >  > ----- >> 410-544-3032 FAX
> >  > ----- >> 412-400-6528 Cell
> >  > ----- >>
> >  > ----- >> -------- Original Message --------
> >  > ----- >> Subject: RE: What is a Bucket Test?
> >  > ----- >> From: "Tom Duross" <[EMAIL PROTECTED]>
> >  > ----- >> Date: Mon, April 14, 2008 11:05 am
> >  > ----- >> To: <[email protected]>
> >  > ----- >>
> >  > ----- >> Back in the late eighties and early nineties,
> >  > ----- >virtually every D and R
> >  > ----- >> system we did or designed got a bucket test. I still
> >  > ----- >have my graduated
> >  > ----- >
> >  > ----- >> buckets and pendent tubes we used. There's a couple of
> >  > ----- >towns here in
> >  > ----- >> MA that still require them. I don't remember being
> >  > ----- >waived on an R
> >  > ----- >> multi-family system back when they were all following
> >  > ----- >what the Cobb
> >  > ----- >> Cty. Chief advised. I seem to remember every one of
> >  > ----- >these systems were
> >  > ----- >
> >  > ----- >> being bucket tested. We never failed a single one but
> >  > ----- >I know some did.
> >  > ----- >>
> >  > ----- >> Tom Duross
> >  > ----- >> Go Red Sox
> >  > ----- >> :)
> >  > ----- >>
> >  > ----- >> I personally don't design SFDs but have seen sprinkler
> >  > ----- >plans for many
> >  > ----- >> of them (and I stayed at a Holiday Inn last night).
> >  > ----- >The architectural,
> >  > ----- >
> >  > ----- >> structural, mechanical plans, etc. are generally very
> >  > ----- >simple and
> >  > ----- >> lacking the type of detail you'd expect on a
> >  > ----- >commercial project.
> >  > ----- >> Likewise, the sprinkler plans tend to be simple -
> >  > ----- >mains & branchlines
> >  > ----- >> drawn as nice strait lines with few or no offsets.
> >  > ----- >Then you get to the
> >  > ----- >
> >  > ----- >> jobsite and, 'Hey, where'd that duct come from. Gotta
> >  > ----- >90 around it."
> >  > ----- >> "Hey, who added the vaulted ceiling, gotta add a
> >  > ----- >couple 90's to get
> >  > ----- >> above it."
> >  > ----- >>
> >  > ----- >> I can think of 2 basic reasons a sprinkler system
> >  > ----- >would fail a bucket
> >  > ----- >> test.
> >  > ----- >> 1) Out of necessity, the fitter installed more pipe &
> >  > ----- >fittings than
> >  > ----- >> the designer calced for.
> >  > ----- >> 2) The underground supply isn't as hydraulically
> >  > ----- >friendly as it's
> >  > ----- >> supposed to be. Small diameter copper (especially the
> >  > ----- >coiled type) is
> >  > ----- >> notorious for being installed with seemingly minor
> >  > ----- >kinks that restrict
> >  > ----- >
> >  > ----- >> water flow.
> >  > ----- >> Pressure losses through meters can be significantly
> >  > ----- >more than many
> >  > ----- >> calcs allow for.
> >  > ----- >>
> >  > ----- >> This takes me back to a recent thread concerning code
> >  > ----- >changes that
> >  > ----- >> will require sprinkler installation in all new SFDs.
> >  > ----- >Just like in Cobb
> >  > ----- >
> >  > ----- >> County, THERE WILL BE A LEARNING CURVE for the new
> >  > ----- >installation
> >  > ----- >> contractors (sprinkler, plumber, or whatever).
> >  > ----- >Designers need to allow
> >  > ----- >
> >  > ----- >> for extra pipe & fitting. Installers need to think
> >  > ----- >ahead & coordinate
> >  > ----- >> so extra pipe & fittings are kept to a minimum.
> >  > ----- >Underground services
> >  > ----- >> have to be installed correctly.
> >  > ----- >>
> >  > ----- >> I personally think bucket tests on 13D installations
> >  > ----- >are a good thing.
> >  > ----- >> Nobody want to do it and nobody wants to fail it.
> >  > ----- >Unfortunately, as in
> >  > ----- >
> >  > ----- >> Cobb County, it becomes part of the 'training' for designers &
> >  > ----- >> installers.
> >  > ----- >> And
> >  > ----- >> when all SFDs require sprinklers, we're going to need
> >  > ----- >a lot of that.
> >  > ----- >>
> >  > ----- >> Ed Kramer
> >  > ----- >> Littleton, CO
> >  > ----- >>> Mike,
> >  > ----- >>>
> >  > ----- >>> Now we are at the heart of the matter. If the bucket
> >  > ----- >test results in
> >  > ----- >>> a surprising number of failures, what is the
> >  > ----- >explanation for this? Is
> >  > ----- >
> >  > ----- >>> it the way the standard is written, is the bucket
> >  > ----- >test technically
> >  > ----- >flawed?
> >  > ----- >>>
> >  > ----- >>> Seems this would be a great senior research project
> >  > ----- >to figure this
> >  > ----- >out.
> >  > ----- >>> I don't understand a surprisingly high failure rate
> >  > ----- >when system
> >  > ----- >>> design is performed by competent FP firms.
> >  > ----- >>>
> >  > ----- >>> Bill Brooks
> >  > ----- >>>
> >  > ----- >>> William N. Brooks, P.E.
> >  > ----- >>>
> >  > ----- >>> It was surprising the number of systems that failed
> >  > ----- >when the test was
> >  > ----- >
> >  > ----- >>> preformed.
> >  > ----- >>>
> >  > ----- >>>
> >  > ----- >>
> >  > ----- >> _______________________________________________
> >  > ----- >> Sprinklerforum mailing list
> >  > ----- >> [email protected]
> >  > ----- >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >  > ----- >>
> >  > ----- >> To Unsubscribe, send an email
> >  > ----- >> to:[EMAIL PROTECTED]
> >  > ----- >> (Put the word unsubscribe in the subject field)
> >  > ----- >>
> >  > ----- >>
> >  > ----- >> _______________________________________________
> >  > ----- >> Sprinklerforum mailing list
> >  > ----- >> [email protected]
> >  > ----- >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >  > ----- >>
> >  > ----- >> To Unsubscribe, send an email
> >  > ----- >> to:[EMAIL PROTECTED]
> >  > ----- >> (Put the word unsubscribe in the subject field)
> >  > ----- >>
> >  > ----- >>
> >  > ----- >
> >  > ----- >_______________________________________________
> >  > ----- >Sprinklerforum mailing list
> >  > ----- >[email protected]
> >  > ----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >  > ----- >
> >  > ----- >To Unsubscribe, send an email
> >  > ----- >to:[EMAIL PROTECTED]
> >  > ----- >(Put the word unsubscribe in the subject field)
> >  > ----- >_______________________________________________
> >  > ----- >Sprinklerforum mailing list
> >  > ----- >[email protected]
> >  > ----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >  > ----- >
> >  > ----- >To Unsubscribe, send an email
> >  > ----- >to:[EMAIL PROTECTED]
> >  > ----- >(Put the word unsubscribe in the subject field)
> >  > ----- >
> >  > ----- >CONFIDENTIAL AND PROPRIETARY:
> >  > ----- >This email message is intended only for the use of the
> >  > ----- >individual or entity to which it is addressed and may
> >  > ----- >contain information that is privileged and confidential,
> >  > ----- >nor is it, unless specifically stated, intended to be
> >  > ----- >relied upon by any person or persons other than the
> >  > ----- >individual or entity named above and no warranties or
> >  > ----- >representations are made or intended to persons or
> >  > ----- >entities not named above.  If the reader is not the
> >  > ----- >intended recipient, you are hereby notified that any
> >  > ----- >dissemination, distribution or copying of this
> >  > ----- >communication is strictly prohibited.  If you have
> >  > ----- >received this communication in error, please notify us
> >  > ----- >immediately by telephone, return this message to the
> >  > ----- >address above and delete all copies.  Thank you.
> >  > ----- >
> >  > ----- >_______________________________________________
> >  > ----- >Sprinklerforum mailing list
> >  > ----- >[email protected]
> >  > ----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >  > ----- >
> >  > ----- >To Unsubscribe, send an email
> >  > ----- >to:[EMAIL PROTECTED]
> >  > ----- >(Put the word unsubscribe in the subject field)
> >  > ----- >_______________________________________________
> >  > ----- >Sprinklerforum mailing list
> >  > ----- >[email protected]
> >  > ----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >  > ----- >
> >  > ----- >To Unsubscribe, send an email
> >  > ----- >to:[EMAIL PROTECTED]
> >  > ----- >(Put the word unsubscribe in the subject field)
> >  > ----- >_______________________________________________
> >  > ----- >Sprinklerforum mailing list
> >  > ----- >[email protected]
> >  > ----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >  > ----- >
> >  > ----- >To Unsubscribe, send an email
> >  > ----- >to:[EMAIL PROTECTED]
> >  > ----- >(Put the word unsubscribe in the subject field)
> >  > ----- >_______________________________________________
> >  > ----- >Sprinklerforum mailing list
> >  > ----- >[email protected]
> >  > ----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >  > ----- >
> >  > ----- >To Unsubscribe, send an email
> >  > ----- >to:[EMAIL PROTECTED]
> >  > ----- >(Put the word unsubscribe in the subject field)
> >  > ----- >
> >  > ----- >_______________________________________________
> >  > ----- >Sprinklerforum mailing list
> >  > ----- >[email protected]
> >  > ----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >  > ----- >
> >  > ----- >To Unsubscribe, send an email
> >  > ----- >to:[EMAIL PROTECTED]
> >  > ----- >(Put the word unsubscribe in the subject field)
> >  >
> >  > _______________________________________________
> >  > Sprinklerforum mailing list
> >  > [email protected]
> >  > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >  >
> >  > To Unsubscribe, send an email to:[EMAIL PROTECTED]
> >  > (Put the word unsubscribe in the subject field)
> >
> >  _______________________________________________
> >  Sprinklerforum mailing list
> >  [email protected]
> >  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >  To Unsubscribe, send an email to:[EMAIL PROTECTED]
> >  (Put the word unsubscribe in the subject field)
> >
> 
> 
> 
> -- 
> Ron Greenman
> at home....
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to