Dear List,

Reading this stream of thought I have lost track of what the concerns are with 
this test.  Is it the time it takes? Is it the difficulty of correcting the 
problem when the test fails?  

We have learned a number of things by  witnessing these tests.  

Sometimes PRV's are upstream of the "T" separating the domestic and sprinkler 
lines.  These have caused the system to fail to be able to deliver the design 
flow. Usually the PRV can be moved to the domestic side of the "T". 

As was mentioned by some writers systems installed not to plans have caused 
systems to fail to be able to deliver the design flow. This was particularly 
acute when we used to see 3/4" cpvc installed.  

We have seen systems fail to deliver the design flows due to undergrounds not 
installed as the sprinkler designer showed. Of course this crosses trade lines. 
It is unclear if the sprinkler contractor has had direct contact with the 
plumbing contractor.

We used to commonly see systems fail to flow the design flow due to debris in 
the heads.  The sprinkler contractors back flushed the  systems to get debris 
out. As a pattern was observed we talked with the building inspectors. We 
discovered that normal plumbing supply lines, or underground from our point of 
view, are not flushed.  The observation is that material just passes through 
plumbing fixtures.*  We now require a UG flush.  It is common to see material 
come out of the line that would not pass a sprinkler head.

Yours,

Bruce Verhei


* If any one out there is having a home built, I think I'd recommend a flush of 
the plumbing supply prior to connection.  My plumbing inspectors might be right 
about debris passing through most fixtures.  I am not so sure of the fridge ice 
maker, or the dishwasher supply.  When I say we see debris sometimes, I mean we 
almost always see some if a trial flush hasn't been done before we get there.  
bv




 -------------- Original message ----------------------
From: "Matthew J. Willis" <[EMAIL PROTECTED]>
> I think it is great that some of the best sprinkler minds in the world, with
> access to the latest technology, can have such an informative and elaborate
> discussion over a 5 gallon bucket. We do require this type of test on
> another system... Do we not do partial flooding test (or full flooding if
> the system isn't shut off quick enough)on our High X foam systems? As Cliff
> pointed out, the pipe or walls shown on the drawings and calcs, are not
> necessarily the ones that end up in the building.
> 
> R/
> 
> Matt 
> 
> Matthew J. Willis
> Living Water Fire Protection, LLC.
> 1160 McKenzie Rd.
> PO Box 877
> Cantonment, FL. 32533
> 850-937-1850 Voice
> 850-937-1852 Facsimile
> [EMAIL PROTECTED]
>  
> 
> ----- >-----Original Message-----
> ----- >From: [EMAIL PROTECTED] 
> ----- >[mailto:[EMAIL PROTECTED] On 
> ----- >Behalf Of Chris Cahill
> ----- >Sent: Tuesday, April 15, 2008 1:25 PM
> ----- >To: [email protected]
> ----- >Subject: RE: What is a Bucket Test? (TIA Needed)
> ----- >
> ----- >So the implied assumption is we will apparently by 
> ----- >default accept systems designed by incompetent, 
> ----- >untrained designers and installed by incompetent 
> ----- >untrained installers and approved by incompetent AHJ's?  
> ----- >I don't like the premise of that.  Perhaps we need a 
> ----- >better system to weed out the incompetence.  
> ----- >
> ----- >But thinking more is this any different in what is 
> ----- >currently going on in the commercial side or large 
> ----- >residential side?  I'd argue adding homes will make it 
> ----- >no worse or better.  There are plenty of trunk slammer.  
> ----- >
> ----- >And unless the premise is wrong (that there is an 
> ----- >abundance of incompetence
> ----- >already) nothing in this discussion has shed light on 
> ----- >why not do all systems (13D, 13R and 13)?  Every 
> ----- >argument for tests in 13D has the same reasoning that 
> ----- >could be applied to any system.  How many AHJ's can tell 
> ----- >the difference between 1 1/2" and 2"?  I know a few can 
> ----- >read but at more than a few feet even that is tough.  
> ----- >Easy substitution and I'd bet you'd get away with it 8
> ----- >out of 10 times.  Bucket test would reveal that.   And 
> ----- >the sad part is IMHO
> ----- >13D's are the easiest to get right.  I mean the hazard 
> ----- >is defined, obstructions are basically not an issue, we 
> ----- >only sprinkler about 1/2 the rooms, no attics or trusses.  
> ----- >
> ----- >This isn't meant to pick on you or Reliable but why do 
> ----- >you sell heads to incompetent companies?  Same could be 
> ----- >asked of all the suppliers.  You're just the lucky one 
> ----- >man enough to be here on a regular basis.  
> ----- >
> ----- >I certainly can't go buy a kitchen hood system without 
> ----- >training from the manufactures which I presume 
> ----- >demonstrates competence. If you don't take offense, 
> ----- >again none meant, could this be an interesting 
> ----- >discussion point.  
> ----- >
> ----- >Chris Cahill, P.E.
> ----- >Fire Protection Engineer
> ----- >Sentry Fire Protection, Inc.
> ----- > 
> ----- >763-658-4483
> ----- >763-658-4921 fax
> ----- > 
> ----- >Email: [EMAIL PROTECTED]
> ----- > 
> ----- >Mail: P.O. Box 69
> ----- >        Waverly, MN 55390
> ----- > 
> ----- >Location: 4439 Hwy 12 SW
> ----- >              Waverly, MN 55390
> ----- >-----Original Message-----
> ----- >From: [EMAIL PROTECTED]
> ----- >[mailto:[EMAIL PROTECTED] On 
> ----- >Behalf Of Mike Brown
> ----- >(TECH- GVL)
> ----- >Sent: Tuesday, April 15, 2008 12:18 PM
> ----- >To: [email protected]
> ----- >Subject: RE: What is a Bucket Test? (TIA Needed)
> ----- >
> ----- >John
> ----- >If you are working in an environment where the projects 
> ----- >are designed by competent, trained designers and 
> ----- >installed by competent trained installers there may not 
> ----- >be a concern that the installation will perform the way 
> ----- >it is designed.  However, should residential sprinklers 
> ----- >be mandated the demand for design and installation will 
> ----- >become much greater than most of our approval agencies 
> ----- >and contractors will be able to handle.  The is more 
> ----- >true in residential situation where the market may be 
> ----- >flooded with "trunk slammers"
> ----- >or unqualified companies doing the residential work. You 
> ----- >would be surprised at the number of sprinkler 
> ----- >contractors that had failures when Cobb County first 
> ----- >started requiring the "Put the Water in The Bucket".  In 
> ----- >many parts of the country the AHJ may know little or 
> ----- >nothing about hydraulics and pretty much approve what is 
> ----- >put in front of him.  The Fire Service will also 
> ----- >experience shortages of trained inspectors if installing 
> ----- >residential sprinkler is mandated for single family 
> ----- >homes.  Several large installer in GA had problems 
> ----- >passing the test when they were first started.
> ----- >
> ----- >Like Cliff, I have said my three dollars worth.  By the 
> ----- >way please purchase my two books from AFSA:  The 
> ----- >leadership Ladder", and "Estimating, Bidding, Selling 
> ----- >and Contracting for Fire Sprinklers."
> ----- >
> ----- >I need to money to retire.
> ----- >
> ----- >Michael L. Brown
> ----- >Manager of Technical Services
> ----- >The Reliable Automatic Sprinkler Company, Inc.'
> ----- >[EMAIL PROTECTED]
> ----- >www.reliablesprinkler.com
> ----- >(864) 843-5228
> ----- >
> ----- >
> ----- >-----Original Message-----
> ----- >From: [EMAIL PROTECTED]
> ----- >[mailto:[EMAIL PROTECTED] On 
> ----- >Behalf Of John Drucker
> ----- >Sent: Tuesday, April 15, 2008 11:57 AM
> ----- >To: [email protected]
> ----- >Subject: RE: What is a Bucket Test? (TIA Needed)
> ----- >
> ----- >Thanks Mike,
> ----- >
> ----- >I understand the concept, however what if a) the job is 
> ----- >installed to plan & calcs b) the job is installed to 
> ----- >revised plans & calcs. ?  What I'm getting at is the 
> ----- >need for the bucket test if the plans and calcs 
> ----- >demonstrate compliance.
> ----- >
> ----- >
> ----- >What I'm getting at is just how reliable are hydraulic 
> ----- >calcs  ? On the surface the bucket test implies that 
> ----- >hydraulic calculations in of themselves are not to be 
> ----- >relied on and that proof of hydraulic performance is 
> ----- >neccesary. If that's the case how about 13R and 13
> ----- >Systems ?.   Its not a water supply "connection" issue 
> ----- >since a main
> ----- >drain test is the accepted method to validate this. 
> ----- >While the bucket test also performs this function, the 
> ----- >need to measure performance in the area of operation 
> ----- >serves no other purpose then to validate hydraulic 
> ----- >design. If it's the installation, i.e. obstructions, 
> ----- >pipe size, sprinkler heads we're concerned about we need 
> ----- >to be flow testing beyond the area of operation.
> ----- >
> ----- >Lastly theres nothing in our adopted codes or standards 
> ----- >that require a "bucket test". Frankly a contractor would 
> ----- >well be within their right to appeal my decision to 
> ----- >require such a test.  Don't take that as I don't believe 
> ----- >theres some validity to "bucket tests", I do, but theres 
> ----- >nothing for me to hang my enforcement hat on and we all 
> ----- >know how contractors insist on "show me in the code."
> ----- >
> ----- >Sincerely,
> ----- >
> ----- >John Drucker
> ----- >Fire Protection Subcode Official (AHJ)
> ----- >New Jersey
> ----- >
> ----- >Safe Buildings Save Lives !
> ----- >
> ----- >
> ----- >
> ----- >-----Original Message-----
> ----- >From: [EMAIL PROTECTED]
> ----- >[mailto:[EMAIL PROTECTED] On 
> ----- >Behalf Of Mike Brown (TECH- GVL)
> ----- >Sent: Tuesday, April 15, 2008 11:19 AM
> ----- >To: [email protected]
> ----- >Subject: RE: What is a Bucket Test? (TIA Needed)
> ----- >
> ----- >John
> ----- >You start with a set of approved plans with the 
> ----- >hydraulic calculations and a permit.  There would be 
> ----- >various stages of inspection depending on the local fire 
> ----- >marshal and the "Bucket" test would be before cover up 
> ----- >of the pipe and fittings. If there have been changes 
> ----- >made to the piping,they should show up on an as-built 
> ----- >drawing (as-built drawings are difficult to get correct 
> ----- >even with commercial systems).  The bucket test would at 
> ----- >least insure that the remote sprinklers flow the minimum 
> ----- >water as per the hydraulic calculations.
> ----- >
> ----- >
> ----- >Michael L. Brown
> ----- >Manager of Technical Services
> ----- >The Reliable Automatic Sprinkler Company, Inc.'
> ----- >[EMAIL PROTECTED]
> ----- >www.reliablesprinkler.com
> ----- >(864) 843-5228
> ----- >
> ----- >-----Original Message-----
> ----- >From: [EMAIL PROTECTED]
> ----- >[mailto:[EMAIL PROTECTED] On 
> ----- >Behalf Of John Drucker
> ----- >Sent: Monday, April 14, 2008 4:03 PM
> ----- >To: [email protected]
> ----- >Subject: RE: What is a Bucket Test? (TIA Needed)
> ----- >
> ----- >Mike,
> ----- >
> ----- >In addition to revised plans and hydraulic calculations 
> ----- >where the job wasn't installed to the original plan ?
> ----- >
> ----- >John Drucker
> ----- >Fire Protection Subcode Official (AHJ)
> ----- >New Jersey
> ----- >
> ----- >
> ----- >-----Original Message-----
> ----- >From: [EMAIL PROTECTED]
> ----- >[mailto:[EMAIL PROTECTED] On 
> ----- >Behalf Of Mike Brown (TECH- GVL)
> ----- >Sent: Monday, April 14, 2008 3:56 PM
> ----- >To: [email protected]
> ----- >Subject: RE: What is a Bucket Test? (TIA Needed)
> ----- >
> ----- >I agree with Thom in that, as we are getting closer to 
> ----- >mandated fire sprinklers in single family homes, the 
> ----- >potential for a large number of new contractors, 
> ----- >plumbers, and assorted others (some of whom may well be 
> ----- >trunk slammers) will be jumping on the bandwagon.  As I 
> ----- >remember when we were getting a licensing law in 
> ----- >Georgia, we had to exempt single family homes in order 
> ----- >to get any kind of law.  In some states there is still 
> ----- >no law at all. (New York State for example has no 
> ----- >licensing law.) This influx of new sprinkler installers 
> ----- >may not be well versed sprinkler installation.  A "Put 
> ----- >the Water in the Bucket" test might well be a good 
> ----- >control measure to protect the potential home owner as 
> ----- >well as protecting the image of our industry.  I would 
> ----- >think that a test like this might be included in the 
> ----- >next edition of NFPA 13D.
> ----- >
> ----- >At least, when I see some of the questions that I get 
> ----- >from some sprinkler contractors and a lot of engineers, 
> ----- >a field test like this could give us some degree of 
> ----- >quality control. That would be a good thing.
> ----- >
> ----- >Something to consider.
> ----- >
> ----- >Michael L. Brown, P.L.L.  (Peon Low Life) Manager of 
> ----- >Technical Services The Reliable Automatic Sprinkler 
> ----- >Company, Inc.'
> ----- >[EMAIL PROTECTED]
> ----- >www.reliablesprinkler.com
> ----- >(864) 843-5228
> ----- >
> ----- >-----Original Message-----
> ----- >From: [EMAIL PROTECTED]
> ----- >[mailto:[EMAIL PROTECTED] On 
> ----- >Behalf Of Thom McMahon
> ----- >Sent: Monday, April 14, 2008 1:39 PM
> ----- >To: [email protected]
> ----- >Subject: Re: What is a Bucket Test? (TIA Needed)
> ----- >
> ----- >This "TEST" was a conditional method when 13D was new. I 
> ----- >have not seen a bucket test that failed, when required, 
> ----- >in the last 15 years.
> ----- >AHJ's are more savvy, Contractors are more cautious, and 
> ----- >know that the field guys will be adding ells. Some just 
> ----- >add extra ells in the calc's and others don't use the 
> ----- >full residual pressure as allowed in 13D. Maybe the 
> ----- >bucket test would be ok if hydraulic calc's are not 
> ----- >required, but is a waste of time and money for Qualified 
> ----- > Designers and layout Tech's, Installers, and AHJ's.
> ----- >
> ----- >Thom McMahon
> ----- >Firetech, Inc.
> ----- >2560 Copper Ridge Dr
> ----- >Steamboat Springs, CO 80488-2136
> ----- >Tel: 970-879-7952
> ----- >Fax: 970-879-7926
> ----- >----- Original Message -----
> ----- >From: <[EMAIL PROTECTED]>
> ----- >To: <[email protected]>
> ----- >Sent: Monday, April 14, 2008 10:05 AM
> ----- >Subject: RE: What is a Bucket Test? (TIA Needed)
> ----- >
> ----- >
> ----- >> Perhaps it is time to incorporate a bucket test 
> ----- >requirement and test 
> ----- >> method into 13D prior to the widespread installation 
> ----- >of these systems 
> ----- >> based on an ICC code change.  If failures are 
> ----- >widespread I think this 
> ----- >> is important enough for a TIA if there's any chance 
> ----- >the ICC will 
> ----- >> reference a current edition of 13D.  The implications 
> ----- >are huge if 
> ----- >> large numbers of 13D systems are expected to fail after being 
> ----- >> engineered and installed by qualified 
> ----- >plumbers/sprinkler companies.
> ----- >>
> ----- >> Bill Brooks
> ----- >>
> ----- >> William N. Brooks, P.E.
> ----- >> Brooks Fire Protection Engineering Inc.
> ----- >> 372 Wilett Drive
> ----- >> Severna Park, MD 21146
> ----- >> 410-544-3620 Phone
> ----- >> 410-544-3032 FAX
> ----- >> 412-400-6528 Cell
> ----- >>
> ----- >> -------- Original Message --------
> ----- >> Subject: RE: What is a Bucket Test?
> ----- >> From: "Tom Duross" <[EMAIL PROTECTED]>
> ----- >> Date: Mon, April 14, 2008 11:05 am
> ----- >> To: <[email protected]>
> ----- >>
> ----- >> Back in the late eighties and early nineties, 
> ----- >virtually every D and R 
> ----- >> system we did or designed got a bucket test. I still 
> ----- >have my graduated
> ----- >
> ----- >> buckets and pendent tubes we used. There's a couple of 
> ----- >towns here in 
> ----- >> MA that still require them. I don't remember being 
> ----- >waived on an R 
> ----- >> multi-family system back when they were all following 
> ----- >what the Cobb 
> ----- >> Cty. Chief advised. I seem to remember every one of 
> ----- >these systems were
> ----- >
> ----- >> being bucket tested. We never failed a single one but 
> ----- >I know some did.
> ----- >>
> ----- >> Tom Duross
> ----- >> Go Red Sox
> ----- >> :)
> ----- >>
> ----- >> I personally don't design SFDs but have seen sprinkler 
> ----- >plans for many 
> ----- >> of them (and I stayed at a Holiday Inn last night). 
> ----- >The architectural,
> ----- >
> ----- >> structural, mechanical plans, etc. are generally very 
> ----- >simple and 
> ----- >> lacking the type of detail you'd expect on a 
> ----- >commercial project.
> ----- >> Likewise, the sprinkler plans tend to be simple - 
> ----- >mains & branchlines 
> ----- >> drawn as nice strait lines with few or no offsets. 
> ----- >Then you get to the
> ----- >
> ----- >> jobsite and, 'Hey, where'd that duct come from. Gotta 
> ----- >90 around it."
> ----- >> "Hey, who added the vaulted ceiling, gotta add a 
> ----- >couple 90's to get 
> ----- >> above it."
> ----- >>
> ----- >> I can think of 2 basic reasons a sprinkler system 
> ----- >would fail a bucket 
> ----- >> test.
> ----- >> 1) Out of necessity, the fitter installed more pipe & 
> ----- >fittings than 
> ----- >> the designer calced for.
> ----- >> 2) The underground supply isn't as hydraulically 
> ----- >friendly as it's 
> ----- >> supposed to be. Small diameter copper (especially the 
> ----- >coiled type) is 
> ----- >> notorious for being installed with seemingly minor 
> ----- >kinks that restrict
> ----- >
> ----- >> water flow.
> ----- >> Pressure losses through meters can be significantly 
> ----- >more than many 
> ----- >> calcs allow for.
> ----- >>
> ----- >> This takes me back to a recent thread concerning code 
> ----- >changes that 
> ----- >> will require sprinkler installation in all new SFDs. 
> ----- >Just like in Cobb
> ----- >
> ----- >> County, THERE WILL BE A LEARNING CURVE for the new 
> ----- >installation 
> ----- >> contractors (sprinkler, plumber, or whatever). 
> ----- >Designers need to allow
> ----- >
> ----- >> for extra pipe & fitting. Installers need to think 
> ----- >ahead & coordinate 
> ----- >> so extra pipe & fittings are kept to a minimum. 
> ----- >Underground services 
> ----- >> have to be installed correctly.
> ----- >>
> ----- >> I personally think bucket tests on 13D installations 
> ----- >are a good thing.
> ----- >> Nobody want to do it and nobody wants to fail it. 
> ----- >Unfortunately, as in
> ----- >
> ----- >> Cobb County, it becomes part of the 'training' for designers & 
> ----- >> installers.
> ----- >> And
> ----- >> when all SFDs require sprinklers, we're going to need 
> ----- >a lot of that.
> ----- >>
> ----- >> Ed Kramer
> ----- >> Littleton, CO
> ----- >>> Mike,
> ----- >>>
> ----- >>> Now we are at the heart of the matter. If the bucket 
> ----- >test results in 
> ----- >>> a surprising number of failures, what is the 
> ----- >explanation for this? Is
> ----- >
> ----- >>> it the way the standard is written, is the bucket 
> ----- >test technically
> ----- >flawed?
> ----- >>>
> ----- >>> Seems this would be a great senior research project 
> ----- >to figure this
> ----- >out.
> ----- >>> I don't understand a surprisingly high failure rate 
> ----- >when system 
> ----- >>> design is performed by competent FP firms.
> ----- >>>
> ----- >>> Bill Brooks
> ----- >>>
> ----- >>> William N. Brooks, P.E.
> ----- >>>
> ----- >>> It was surprising the number of systems that failed 
> ----- >when the test was
> ----- >
> ----- >>> preformed.
> ----- >>>
> ----- >>>
> ----- >>
> ----- >> _______________________________________________
> ----- >> Sprinklerforum mailing list
> ----- >> [email protected]
> ----- >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> ----- >>
> ----- >> To Unsubscribe, send an email
> ----- >> to:[EMAIL PROTECTED]
> ----- >> (Put the word unsubscribe in the subject field)
> ----- >>
> ----- >>
> ----- >> _______________________________________________
> ----- >> Sprinklerforum mailing list
> ----- >> [email protected]
> ----- >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> ----- >>
> ----- >> To Unsubscribe, send an email
> ----- >> to:[EMAIL PROTECTED]
> ----- >> (Put the word unsubscribe in the subject field)
> ----- >>
> ----- >>
> ----- >
> ----- >_______________________________________________
> ----- >Sprinklerforum mailing list
> ----- >[email protected]
> ----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> ----- >
> ----- >To Unsubscribe, send an email
> ----- >to:[EMAIL PROTECTED]
> ----- >(Put the word unsubscribe in the subject field) 
> ----- >_______________________________________________
> ----- >Sprinklerforum mailing list
> ----- >[email protected]
> ----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> ----- >
> ----- >To Unsubscribe, send an email
> ----- >to:[EMAIL PROTECTED]
> ----- >(Put the word unsubscribe in the subject field)
> ----- >
> ----- >CONFIDENTIAL AND PROPRIETARY:
> ----- >This email message is intended only for the use of the 
> ----- >individual or entity to which it is addressed and may 
> ----- >contain information that is privileged and confidential, 
> ----- >nor is it, unless specifically stated, intended to be 
> ----- >relied upon by any person or persons other than the 
> ----- >individual or entity named above and no warranties or 
> ----- >representations are made or intended to persons or 
> ----- >entities not named above.  If the reader is not the 
> ----- >intended recipient, you are hereby notified that any 
> ----- >dissemination, distribution or copying of this 
> ----- >communication is strictly prohibited.  If you have 
> ----- >received this communication in error, please notify us 
> ----- >immediately by telephone, return this message to the 
> ----- >address above and delete all copies.  Thank you.
> ----- >
> ----- >_______________________________________________
> ----- >Sprinklerforum mailing list
> ----- >[email protected]
> ----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> ----- >
> ----- >To Unsubscribe, send an email
> ----- >to:[EMAIL PROTECTED]
> ----- >(Put the word unsubscribe in the subject field) 
> ----- >_______________________________________________
> ----- >Sprinklerforum mailing list
> ----- >[email protected]
> ----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> ----- >
> ----- >To Unsubscribe, send an email
> ----- >to:[EMAIL PROTECTED]
> ----- >(Put the word unsubscribe in the subject field) 
> ----- >_______________________________________________
> ----- >Sprinklerforum mailing list
> ----- >[email protected]
> ----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> ----- >
> ----- >To Unsubscribe, send an email 
> ----- >to:[EMAIL PROTECTED]
> ----- >(Put the word unsubscribe in the subject field) 
> ----- >_______________________________________________
> ----- >Sprinklerforum mailing list
> ----- >[email protected]
> ----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> ----- >
> ----- >To Unsubscribe, send an email 
> ----- >to:[EMAIL PROTECTED]
> ----- >(Put the word unsubscribe in the subject field)
> ----- >
> ----- >_______________________________________________
> ----- >Sprinklerforum mailing list
> ----- >[email protected]
> ----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> ----- >
> ----- >To Unsubscribe, send an email 
> ----- >to:[EMAIL PROTECTED]
> ----- >(Put the word unsubscribe in the subject field)
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)