Hello Bobby,

I was taught if there is a 5th floor it is not 13R. The whole building has
to be 13.

Friday, April 18, 2008, 8:16:04 AM, you wrote:

> A question has been asked in our office and I would appreciate the opinions
> of the forum as to the intent of 13R. 

>  There is a 5 story building, bottom floor is mercantile and the top 4
> floors are residential. "NFPA13R Standard for the Installation of Sprinkler
> Systems in Residential Occupancies up to and Including Four Stories in
> Height." The debate is; is the intent of the standard to be that anything
> over 4 stories cannot be classified as 13R or can the building in question
> be classified as 13R because there are 4 stories in height for residential
> occupancy? 

>  

> Thank you in advance.

>  