Thank you for your responses I believe you settled our debate although now
they are asking me "... where are they getting you have to stay within one
standard?" (13 or 13R).
Thanks again.
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton
Sent: Friday, April 18, 2008 10:17 AM
To: [email protected]
Subject: RE: 13R Classification
There is a proposal in the current ROP (13R-58, Log #37 - Committee
Action: Accept) that will hopefully give better direction with regard to
this (these) issue(s). Capsule version of the material is to clarify
that if a building (such as a pedestal or podium type) is divided into
separate buildings as defined by the code, that 13R is applicable in the
R-group building and 13 would apply to the other. This represents a
change from what we've been saying (myself, AFSA, here in this thread)
WRT to "mixed use" buildings requiring a 13 design unconditionally.
But the proposed language makes very clear that these provisions apply
to buildings that are no more than 4 stories above "grade plane" (also
as defined by the code), so if we're talking about a 5-story structure
(per code), the applicable standard is 13. Period.
Steve Leyton
Protection Design & Consulting
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Friday, April 18, 2008 6:53 AM
To: [email protected]
Subject: RE: 13R Classification
Could you consider this 2 separate areas if the building falls under the
"pedestal" design of section 508 (2003 IBC)? I have an excerpt from the
2006 Building Safety Journal that may help.
"In addition to the basic requirement that the pedestal
building be of Type IA construction and separated from the
buildings above by a horizontal ceiling/floor/roof assembly
having a minimum 3-hour fire resistance rating, the following
limitations also apply.
* Per Section 508.2, Item 4, Exceptions, the use of the
pedestal building is restricted to any combination of the
following:
* S-2 enclosed parking garage;
* multiple Group A uses limited to those having assembly
rooms with occupant loads of less than 300 each;
* Group B uses;
* Group M uses; and
* entry lobbies, mechanical rooms, storage areas and
similar uses incidental to the operation of the building.
* Per Section 508.2, Item 3, the use of the buildings above
the pedestal building is restricted to any combination of
the following:
* Group R uses,
* multiple Group A uses limited to those having assembly
rooms with occupant loads of less than 300 each,
* Group B uses and
* Group M uses. "
Hope this helps. Bobby, leave me email if you want the full article.
Thanks,
Dewayne Martinez, CET
Design Build Fire Protection
[EMAIL PROTECTED]
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tom
Duross
Sent: Friday, April 18, 2008 7:55 AM
To: [email protected]
Subject: RE: 13R Classification
Plus, it's mixed use. 13 throughout.
One building, one use, one standard, one design.
Tom
GRS
Hello Bobby,
I was taught if there is a 5th floor it is not 13R. The whole building
has to be 13.
Friday, April 18, 2008, 8:16:04 AM, you wrote:
> A question has been asked in our office and I would appreciate the
opinions
> of the forum as to the intent of 13R.
> There is a 5 story building, bottom floor is mercantile and the top 4
> floors are residential. "NFPA13R Standard for the Installation of
Sprinkler
> Systems in Residential Occupancies up to and Including Four Stories in
> Height." The debate is; is the intent of the standard to be that
> anything over 4 stories cannot be classified as 13R or can the
> building in question be classified as 13R because there are 4 stories
> in height for residential occupancy?
>
> Thank you in advance.
>
> Bobby Gillett
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)