Replace your main floor mercantile occupancy with a residential occupancy.
Now you have a less hazardous building. Would you design the 5 storey
residential building to 13R? If you design the 5 storey residential building
to 13, you should not use 13R, a less stringent standard when you increase
the hazard, by having a mercantile floor.

Tony

Tony

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bobby Gillett
Sent: April 18, 2008 6:16 AM
To: [email protected]
Subject: 13R Classification

A question has been asked in our office and I would appreciate the opinions
of the forum as to the intent of 13R. 

 There is a 5 story building, bottom floor is mercantile and the top 4
floors are residential. "NFPA13R Standard for the Installation of Sprinkler
Systems in Residential Occupancies up to and Including Four Stories in
Height." The debate is; is the intent of the standard to be that anything
over 4 stories cannot be classified as 13R or can the building in question
be classified as 13R because there are 4 stories in height for residential
occupancy? 

 

Thank you in advance.

 

Bobby Gillett

Project Manager

[EMAIL PROTECTED]

(731)-424-0130

   

 

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to