A couple of observations:

Using a relief valve to regulate pressure is a bad idea. Relief valves generally are designed to open at a set pressure, but not necessarily to close at that pressure. They They are emergency devices, intended to operate only if the driver over speeds. To regulate pressure, use a pressure regulating valve.

Feeding the discharge from a relief valve back into the pump suction won't accomplish what is intended. It's sort of like trying to pick yourself up by your bootstraps. What will happen if you run the pump with no flow is that the relief valve will open,water will circulate and reach equilibrium at a pressure higher than the relief valve setting.

Yt's thought by many that it is better to put the PRV on the discharge side of the pump because, if there is a problem, the higher pressure will be more likely to clear it. There really isn't a good reason to put a PRV on the suction side.

Joe