Ok, I'm catching up after some time away and some time off.
My recollection in the late-80's was the condensation would come down to the
check and form an ice plug, which would mean no water to that section of the
dry system. "Gluing" a clapper in place would be similar, but wasn't what I
heard in Phila at the time.

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman
Sent: Thursday, April 10, 2008 12:27 PM
To: [email protected]
Subject: Re: Check valves and dry systems

Todd,

That was what I was talking about in my last post. You cannot  
subdivide the dry piper with check valves. One reason I can think of  
is because when new and they work you have one water delivery time but  
as they age and leak each subdivision that does so adds time to  
decompression and so to water delivery also. I've seen this problem  
and so from this standpoint this recent (maybe 99) in 13 makes sense.  
The other problem I can imagine is the clapper on a swing check  
"glueing" itself shut due to disuse.On the one's I'm familiar with  
that was never a problem.

Back to subdivision. 13 does not (and I admit I'm stretching this and  
remember that I don't like the idea but I'm not the owner, designer,  
layout tech or the AHJ and am merely arguing code/standard points)  
prohibit check valves in dry systems. It specifically prohibits using  
them for subdivision. Again, if water delivery time was what prompted  
the prohibition, then testing the system with the check valves removed  
and replaced by spools effectively addresses the prohibition since the  
now missing clappers are not there to hold air back and so you are  
getting a realistic picture of the entire system rather than just the  
riser and one floor.

Would IU recommend such a scheme. Never, but not because the schema  
itself is without logical merit but rather because of the ridiculous  
costs and the tendency to "cheat" associated with IT&M.

Part of the argument here revolves around committee intent. Why is  
this rule there in the first place (like the 52K square footage  
limitation)? Is it there because it's always been there and we don't  
remember why (Like 52K)? Is it there because a problem was discovered  
and this is a fix (maybe like this prohibition against subdivision by  
check valve in dry pipes)? Is it there because some vendor has come  
out with a new product that meets a need and rules for its use are  
needed (the section for ESFR)? Or is it there because someone can just  
make money? We can't know unless we religiously follow the RFPs/RFCs  
and the voting and have photographic memories or wish to spend hours  
upon hours searching old stuff that's not catalogued or indexed.  
Perhaps with the state of electronic filing NFPA can make access to  
the thousands of hours of committee stuff easily accessible. I don't  
think the intent is to make these deliberations opaque in any way but  
they are, at this time, translucent at best.

We have Joe Hankins that can shed light on some of FM reasons and  
conclusions. Steve addresses 14 intent regularly. Bamford, Dead Bob,  
Roland (my neighbor that I never see) and others chime in when they  
know how a committee came to a decision but these guy's memory hardly  
make an archive.

Ron Greenman