I started this a couple of emails ago but I'll finish it here.

I don't particularly like the arrangement Randy wants but the question
is can it be done. You don't have to use a floor control assembly. You
do need valves and check valves, and you'd need a drain downstream of
the check of course. There is nothing I know of that requires floor
zoning of alarms in this size building so only tampers on the control
valves would be necessary.

Randy, I don't see how you can eliminate the requirement for check valves.

Todd, although you can't use check valves to segregate sections of the
system you have to have the check valves. Two separate requirements.
One has to do with isolating the floor for service. The other has to
do with water delivery time.

Bill, if you can't meet water delivery time without the check valves
(test the system with spool pieces replacing the check valves during
the testing) then you have failed another requirement. This whole idea
may fall apart on the time it takes to drop this size system through
an inspectors test port.

Randy, unless you can think of a simpler method of testing water
delivery time in some other method than dropping the system, replacing
the checks with spools, bringing the system back up, testing,
draining, replacing the checks and re-establishing full service then I
think that IT&M will either: 1. be too expensive to justify the
initial savings on installation or 2, not be done properly due to
difficulty and cost.

I think I'd go with manual wet combined (if possible) or two separate
systems. This has been a nice simple exercise in design rather than
layout.



On Wed, Apr 9, 2008 at 6:26 PM,  <[EMAIL PROTECTED]> wrote:
> It looks like a dry standpipe system is OK by 2006 IBC 905.8.  I've
>  tested one of these.  The trip time and water delivery time is very
>  short when you open a 2 1/2" valve on a 200 ft piece of 4" pipe.
>
>  However, I would wonder how you will meet the time to end head
>  requirement when you use the same dry valve for four stories.  If you
>  choose to use check valves at each floor (as is required for wet
>  combined systems), then the reliability of these valves could be called
>  into question by the AHJ since check valves are not permitted to divide
>  dry systems.
>
>  It doesn't look like this would be acceptable.
>
>  Bill Brooks
>
>  William N. Brooks, P.E.
>  Brooks Fire Protection Engineering Inc.
>  372 Wilett Drive
>  Severna Park, MD 21146
>  410-544-3620 Phone
>  410-544-3032 FAX
>  412-400-6528 Cell
>
>
>
>  -------- Original Message --------
>  Subject: Dry standpipe and dry systems.
>  From: "Randy Knutson" <[EMAIL PROTECTED]>
>  Date: Wed, April 09, 2008 6:51 pm
>  To: <[email protected]>
>
>  Forum Members,
>
>
>
>  I have a two part question.
>
>  1. Can I have a combined standpipe on a dry system? I have 4 story
>  factory
>  building that's not heated. Fourth floor is above 30 feet so I need a
>  standpipe. I have a heated pump room with a dry pipe valve. I was first
>  looking at the project with a dry manual standpipe and a separate dry
>  sprinkler system riser. I would like to combine the two and save piping
>
>
>
>  2. Is it OK to put floor control valves in on dry pipe system? There is
>  a
>  removable section of roof where they take equipment out. I would like to
>  give the facility the ability to shut individuals floors down for
>  modification to the systems.
>
>
>
>  Thanks,
>
>
>
>  Randy Knutson
>
>  Shilo Automatic Sprinkler, Inc.
>
>  _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  To Unsubscribe, send an email
>  to:[EMAIL PROTECTED]
>  (Put the word unsubscribe in the subject field)
>
>
>  _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  To Unsubscribe, send an email to:[EMAIL PROTECTED]
>  (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....