I didn't look at #13-07.
If indeed the only requirement for galv in your adopted standard requires
galv in large-drop systems, then despite the (obvious) conflicts Craig is
sorting thru, then yes, only large drop systems are affected in a manner
which the TC believes needed a requirement for galv, others don't. 

So from what I see before me, and I didn't open the referenced standard,
unless you have LDs you don't need galvanized. Naturally it may be less to
use galv than a pump if the dif in C factors helps you across the line
between gravity and boost.... but in meeting the minimum consensus
standard's requirements, go black and don't look back. We use galv simply
because we think it is the right thing to do, and only refrain upon specific
direction from whom we're contracted with- nothing to do with compliance
with minimum consensus standards. Most people don't hydro at 225-265 PSI
either.

Naturally there's that great blurb in the specs that requires meeting
requirements of the Owner's insurance carrier who remains anonymous, so you
have no clue as to what those requirements might be! 

glc