Randy,

I'm not sure I agree with a couple of the responses you've received, so I'll weigh in with my own.

The values shown in Table 9.1.1.6.1(b) in the '02 edition of NFPA-13 are based on the required section modulus for a load created by 15'-0" of pipe filled with water, plus 250 pounds, and a maximum allowable bending stress of 15.0 ksi. (This is from note #2 of that table). So far so good.

The formula they use for this simple beam calculation is directly from the AISC manual, beam diagram #7, and shows the calculation for the maximum moment of inertia (Mmax) as the result of PL/4, where P is the load in pounds, and L is the length of the beam in inches. In the case of what you're describing the P is approximately 426.7# (based on weight of 4" sch 10 as 11.78 lb/ft x 15' and 250#), and the
value for L is 168" (14' x 12" per foot).

The resulting maximum moment of inertia (Mmax) is then 17,921.4 inch-pounds, or 17.921 kips.

The maximum allowable bending stress (Fb) is established by NFPA-13 as 15.0 ksi (or 15,000 pounds per square inch), so you would simply divide Mmax by Fb, or 17.921 kips by 15.0 ksi, resulting in a minimum required section modulus of 1.1947 in^3. So you're assumption is basically correct.

For proof, just do the math on the same weight (426.7#) with a 120" (10') span, and you'll come up with a required section modulus of at least 0.8534 in^3, which is awfully close to the value shown in
NFPA-13.

As for Ray's comment, I'm in agreement, if you can figure out a way to use the trapeze with the load not centered you can reduce the equivalent length of the span using the formula in A.9.1.1.6, which uses 4AB/A+B to reach an equivalent length if the load is not centered. In the trap you're describing if the load was 11'-0" from one end and 3'-0" from the other this would work out to an
equivalent length of about 9.4', as a result of (4x11'x3')/14'

I'm completely in agreement with Todd on this one though, I'd be sure and get a structural PE to sign off on the math. You're not required to have a PE behind your name to think these thoughts or even to do the math, however it would be a prudent course of action to protect yourself by
getting one to carefully review it and sign off.

Just some thoughts on your question.  Hope that helps.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
IMPORTANT NOTICE: This correspondence is not a Formal
Interpretation issued pursuant to NFPA Regulations. Any opinion
expressed is the personal opinion of the author and does not necessarily
represent the official position of the NFPA or its Technical Committees.
In addition, this correspondence is neither intended, nor should it be
relied upon, to provide professional consultation or services.


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Matthew
J. Willis
Sent: Tuesday, May 20, 2008 12:25 PM
To: [email protected]
Subject: RE: Trapeze lengths beyond 10'-0"

Can you apply the formula and get an equivalent modulus based on not
center loading the members?

R/

Matt

Matthew J. Willis
Living Water Fire Protection, LLC.
1160 McKenzie Rd.
PO Box 877
Cantonment, FL. 32533
850-937-1850 Voice
850-937-1852 Facsimile
[EMAIL PROTECTED]
----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On
----- >Behalf Of Randy Knutson
----- >Sent: Tuesday, May 20, 2008 11:05 AM
----- >To: [email protected]
----- >Subject: Trapeze lengths beyond 10'-0"
----- >
----- >Forumites,
----- >
----- >
----- >
----- >I searched the archives and didn't find a discussion on
----- >this topic.
----- >
----- >Here's my question?
----- >
----- >
----- >
----- >Can I extrapolate out beyond the 10'-0" length on the
----- >section modulus required for trapeze in table
----- >9.1.1.6.1(a) '07ed.?
----- >
----- >
----- >
----- >A fitter called this morning wanting 14' trapeze hangers
----- >for 4" pipe. He was placing the main in the wrong
----- >location but it brought up an interesting question. I
----- >noticed that the section modulus has a linear increase
----- >with trapeze length.
----- >
----- >For 4" Sch 10 y=.085x, where y=section modulus &
----- >x=Trapeze length. So, for a 14' trapeze for 4" sch 10,
----- >would a 1.19 section modulus work?
----- >
----- >Do I have to have the initials PE after my name to think
----- >these thoughts?
----- >
----- >
----- >
----- >Thanks,
----- >
----- >
----- >
----- >Randy Knutson
----- >
----- >Shilo Automatic Sprinkler, Inc.
----- >
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to