Chuck, Without knowing you adopted code the model codes require all valves capable of controlling water supply to sprinklers, hose valves, pumps, etc to be supervised electrically.
Heres an IBC reference; 903.4 John Drucker Fire Protection Subcode Official (AHJ) New Jersey -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of RFI - Bismarck Sent: Wednesday, May 21, 2008 10:40 AM To: [email protected] Subject: Sectional Valves... I think I asked this already... and apologize for regurgitating it! I have a bldg. that is 'U-shaped' in nature. The system is of CPVC in nature - fairly small. Prior to going into the 'legs' of the 'U' - the contractor wants to have (2) ball valves installed to isolate each wing for maintenance purposes. Do these ball valves need to be of a 'monitored' (wired to panel) type or can they be just run-of-the-mill ball valves? Imho - I believe they should be 'monitored' valves. Thanks! R.F.P. Chuck No virus found in this outgoing message. Checked by AVG. Version: 7.5.524 / Virus Database: 269.23.21/1458 - Release Date: 5/21/2008 7:21 AM CONFIDENTIAL AND PROPRIETARY: This email message is intended only for the use of the individual or entity to which it is addressed and may contain information that is privileged and confidential, nor is it, unless specifically stated, intended to be relied upon by any person or persons other than the individual or entity named above and no warranties or representations are made or intended to persons or entities not named above. If the reader is not the intended recipient, you are hereby notified that any dissemination, distribution or copying of this communication is strictly prohibited. If you have received this communication in error, please notify us immediately by telephone, return this message to the address above and delete all copies. Thank you. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)