Chuck,

Without knowing you adopted code the model codes require all valves
capable of controlling water supply to sprinklers, hose valves, pumps,
etc to be supervised electrically.

Heres an IBC reference; 903.4

John Drucker
Fire Protection Subcode Official (AHJ)
New Jersey

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of RFI -
Bismarck
Sent: Wednesday, May 21, 2008 10:40 AM
To: [email protected]
Subject: Sectional Valves...

 

I think I asked this already... and apologize for regurgitating it!  I
have a bldg. that is 'U-shaped' in nature.  The system is of CPVC in
nature - fairly small.  Prior to going into the 'legs' of the 'U' - the
contractor wants to have (2) ball valves installed to isolate each wing
for maintenance purposes.  Do these ball valves need to be of a
'monitored' (wired to panel) type or can they be just run-of-the-mill
ball valves?

 

Imho - I believe they should be 'monitored' valves.  Thanks!

 

R.F.P. Chuck

 


No virus found in this outgoing message.
Checked by AVG. 
Version: 7.5.524 / Virus Database: 269.23.21/1458 - Release Date:
5/21/2008
7:21 AM
 
  

CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to