Mark,

I only mentioned the attic sprinklers as perhaps a better alternative to the suggestion for sidewall sprinklers at the peak. I don't know of anything that has been tested in such a steep pitch.

Joe

Eckard, Mark - Mark E wrote:
Joe,

Per the Tyco data sheet the BB type attic sprinklers are only listed for
up to 100% rise over run (12:12 pitch).  Is there another sprinkler that
can do this in a 28:12 pitch? Or is the some additional data for these
sprinklers?
Mark E. Eckard S.E.T.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe
Hankins
Sent: Friday, May 23, 2008 2:28 PM
To: [email protected]
Subject: Re: steep pitch roofs

Could you use Attic sprinklers at the peak? They accomplish the same intent as sidewalls at the peak, and have actually been tested in that configuration.

Joe

Todd Williams - FPDC wrote:
I am working on a historic church sanctuary with a pitch of approximately 28/12. The arrangement calls for branch lines to be symmetrical on each side, similar to NFPA 13 (2002) figure 8.6.4.1.3.1(b). I can meet the requirements for the steeply pitched roof section 8.6.4.1.3.3 and my "S" distance over the peak is good, but my straight line distance between sprinklers would be less than 6 ft and the deflectors would be effectively pointing the discharge towards the sprinkler on the opposite side. I think I have a problem here, but I am not sure how to address it. Any thoughts?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to