There has been very, very little testing with sloped roofs. The problem with your idea is that simply flowing water from a sprinkler and seeing if it hits an adjacent one doesn't answer the skipping question. It has to be done under actual fire conditions. It is the combination of the fire plume and discharge (and the resulting cooling at adjacent sprinklers) that determines if skipping will occur. (the 6 ft distance has not been determined to work. it was chosen years ago more or less arbitrarily. In fact, in actual fire tests, severe skipping has occurred many times with spacing greater than 6 ft, and baffles were of little help in those situations.)

The dilemma with this application is not skipping due to discharge from adjacent sprinklers, but getting sprinklers to operate . Any approach that does not include a line of sprinklers at the roof peak is very unlikely to be effective. Sometimes you have to just accept that NFPA 13 doesn't address all situations you're going to see in the field and you have to kick it back to the architect/engineer to decide what they want.

Joe

Todd Williams - FPDC wrote:
I had another thought. How much testing has been done on pitched roofs? There has to be a point where sprinklers impact each other when the deflectors are not parallel and it is probably a function of angle and distance. When the deflectors area parallel, the 6 ft distance has been determined as an acceptable minimum. As the angle between deflectors increases and the spray starts to point towards adjacent heads, would the acceptable distance likewise increase? You have spray that is pointing at adjacent sprinklers and at some angle, interference is going to occur. This would occur with both arrangements in 8.6.4.1.3.1. Any thoughts?




At 10:09 PM 5/23/2008, you wrote:
Todd,

Nothing, to my knowledge, is approved for such a steep slope. I suggested the attic sprinklers in response to the suggestion for sidewall sprinklers at the peak. My only intent was to suggest that, if you're going to go beyond the defined limits of a type of sprinkler, you should at least start with a type that at least is intended to work in a similar application. I can't say that the attic sprinklers will work, but if they won't, sidewall sprinklers at the peak certainly won't work either.

Joe

Todd Williams - FPDC wrote:
Joe, Attic sprinklers aren't approved for slopes greater then 12:12 and I have about 28:12. Also, I didn't think you could use attic sprinklers in occupied spaces.

This is an occupied space (church sanctuary) not a concealed one. Also, this is a historic building (c. 1859) and is very architecturally sensitive. The pipe is exposed and soffits and baffles are not an option.


At 02:27 PM 5/23/2008, you wrote:
Could you use Attic sprinklers at the peak? They accomplish the same intent as sidewalls at the peak, and have actually been tested in that configuration.

Joe

Todd Williams - FPDC wrote:
I am working on a historic church sanctuary with a pitch of approximately 28/12. The arrangement calls for branch lines to be symmetrical on each side, similar to NFPA 13 (2002) figure 8.6.4.1.3.1(b). I can meet the requirements for the steeply pitched roof section 8.6.4.1.3.3 and my "S" distance over the peak is good, but my straight line distance between sprinklers would be less than 6 ft and the deflectors would be effectively pointing the discharge towards the sprinkler on the opposite side. I think I have a problem here, but I am not sure how to address it. Any thoughts?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to