If the present system is a wet system, you may want to consider changing it 
over to a single interlock preation system.  Single interlock systems are used 
in water sensitive environments and contain air pressure within the system 
piping for monitoring pipe integrity.  Should a sprinkler or the system piping 
become damaged, only air pressure will be released providing a supervisory 
alarm, since the valve will not trip.  The valve will trip only if the 
detection system is activated.  This will only place water in the piping and no 
water will discharge until the sprinkler operates.

Detection systems such as air aspirating systems, or that utilize cross zoning 
are ways to ensure that there is an actual fire incident warranting the valve 
to trip.

With a gaseous system, the integrity of the room must be maintained, and 
usually a preaction system as a back-up may be required.

Regards,

Salvatore Izzo, P.E. SFPE
Manager - Reliable Technical Services

________________________________________
From: [EMAIL PROTECTED] [EMAIL PROTECTED] On Behalf Of Haji, Jaber M [EMAIL 
PROTECTED]
Sent: Monday, June 23, 2008 8:44 AM
To: [email protected]
Subject: worried about Sprinklers leakage

Newly constructed research and development lab facility is protected by a wet 
type sprinkler system, one of the lab scientist is worried about the accidental 
release of the automatic sprinkler  heads on top  or  in the  vicinity of the 
high tech., expensive analytical instruments such as NMR, FTMS, autospec GC/MS 
and ESEM , which present a potential risk of damage to these instruments in 
case these sprinklers kick off during actual emergency or broken by mistake by 
a maintenance personnel or a lab personnel.  He suggests gas suppression 
instead. I explained to him that accidental leakage of wet type sprinkler 
system is very minimal. The question is what the probability of activation and 
how much will it cost to replace the existing system with a gas suppression 
system.  Your recommendations/insights are highly appreciated.
Jaber Al-Haji
[EMAIL PROTECTED]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to