Haji

Stick with the sprinklers - gas systems discharge due to spurious sensor
actuations, lightning and other stimuli. I know that it can be difficult to
source replacement gas supplies in the Kingdom and the cost and delay could
impair the lab's mission.

If you really are worried about sprinkler heads being hit by accident then
by all means consider recessed or institutional heads.  If you are really
worried about spurious actuation of sprinklers go to a pre- action system.

Don't worry about electrical issues - IBM sprinkle all their labs, workshops
and factories !

Masalaama !

Stewart

Stewart Kidd
Loss Prevention Consultancy Ltd UK

On 23 Jun 2008, at 13:44, Haji, Jaber M wrote:

> Newly constructed research and development lab facility is protected 
> by a wet type sprinkler system, one of the lab scientist is worried 
> about the accidental release of the automatic sprinkler  heads on top  
> or  in the  vicinity of the high tech., expensive analytical 
> instruments such as NMR, FTMS, autospec GC/MS and ESEM , which present 
> a potential risk of damage to these instruments in case these 
> sprinklers kick off during actual emergency or broken by mistake by a 
> maintenance personnel or a lab personnel.  He suggests gas suppression 
> instead. I explained to him that accidental leakage of wet type 
> sprinkler system is very minimal. The question is what the probability 
> of activation and how much will it cost to replace the existing system 
> with a gas suppression system.  Your recommendations/insights are 
> highly appreciated.
> Jaber Al-Haji
> [EMAIL PROTECTED]
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email 
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to