No help, we are on our own.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - FPDC
Sent: Tuesday, June 24, 2008 7:37 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Sand or silt clogging strainers

Would the local fire department be any help in getting this thing
flushed?


At 10:18 AM 6/24/2008, you wrote:
>We have 1500 gpm diesel pump equipped with a PLD. While running at full
>flow the strainers to the PLD and in the cooling line become clogged
>with sand or fine silt causing the engine to over heat and the PLD to
>fail. The city pressure and volume is not sufficient to adequately
flush
>the 16" dead end main coming to the site so we have to live with the
>contaminated water for the time being. We are going to install a
>strainer in the suction to the pump but that will only catch rocks and
>stuff not the sand and silt.
>
>The problem is how to flush or prevent the strainers from clogging
>during a pump run. I have heard of cyclonic generator as a possible
>solution but have not been able to find and information on one.
>
>We are looking for ideas, suggestions or proven solutions if there are
>any.
>
>Thanks for your help.
>
>Ron Fletcher
>Aero Automatic
>Phoenix, AZ
>_______________________________________________
>Sprinklerforum mailing list
>Sprinklerforum@firesprinkler.org
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email
to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to