Sounds like tank time (at least for the sprinkler)
At 11:17 AM 7/9/2008, you wrote:
Thanks! We will have a pump but...the water
supply (gpm) seems too low for the demand
especially factoring in hose allowance.
David Bryan
fpii
-----Original Message-----
From: Todd Williams - FPDC <[EMAIL PROTECTED]>
To: [email protected]
Sent: Wed, 9 Jul 2008 10:55 am
Subject: Re: Water supply question
Without doing any engineering and no other
information, I would say probably not. According
to A.5.6.3, cartoned carpet tiles are a Group A
plastic. The latex foam pads are another bundle
of joy. 55psi may not be enough to handle the
demand. More engineering is needed on this
project to make an actual determination.
(Disclaimer: my opinion only and may not have any basis in fact)Â
Â
Â
At 10:10 AM 7/9/2008, you wrote:Â
Â
>I am looking at a 25,000 sq foot
former >manufacturing facility that is being
renovated >and a wet system is being
provided.Ã A storage >area- 4700 sq ft. willÃ
contain rolled upà rugs >(nylon type à and
latex foam pads) that will be >stored on 12
foot high racks along with boxes of >water
based adhesive and carpet tiles. The >storage
area has a 20 foot high ceiling with >30âÂ
steel joists and masonry constructioon.Ã
I >was told that by an outside source that
FM >Global has design criteria for this type of material.Â
>Problem is the water supply is 55 static and
45 >at 920 gpm residual. and 1808 gpm à at 20
psi >(this was projected by the water provider.).Â
>Â
>I am questioning whether this is enough
water >for this type of hazard. Any thoughts?Â
>Â
>David BryanÂ
>fpiiÂ
>_______________________________________________Â
>Sprinklerforum mailing listÂ
>[EMAIL PROTECTED]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforumÂ
>Â
>To Unsubscribe, send an email to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)Â
Â
Todd G. Williams, PEÂ
Fire Protection Design/ConsultingÂ
Stonington, ConnecticutÂ
www.fpdc.comÂ
860.535.2080 _______________________________________________Â
Sprinklerforum mailing listÂ
[EMAIL PROTECTED]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforumÂ
Â
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)Â
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)