I kind of go along with the comments that this should not be parked under a grandstand, especially when occupied. If this thing is moved, I would look into some form of self-contained protection, such as a dry chemical. But the purpose would only be to keep the combustible construction from igniting the fireworks. Why don't they get a container and put it on a trailer? At least that is all metal and would eliminate the wood construction.

At 04:54 AM 7/15/2008, you wrote:

----- Original Message ----- From: " douglas hicks" <[EMAIL PROTECTED]>
To: "sprinkler board" <[email protected]>
Sent: Monday, July 14, 2008 3:03 PM
Subject: Explosives


I have a customer who stores a quantity of less than 2 # of Class 1.4G explosives. These explosives are comparable to fireworks. The 1.4G is stored in a metal cabinet, not rated. The storage unit is 8 foot wide x 8 foot high x 12 foot long. The construction is wood frame, plywood floor, wood panel interior, and metal outside. If this sounds like a job trailer, your are right. The trailer is parked under a grandstand. the steel/wood grandstand is protected with a dry system, under the grandstands. Other contents are ordinary combustibles, wood, paper, cardboard.

Upon occasion, the trailer is moved to other locations for shows. Then the trailer is parked under the grandstand. unless the trailer is put in the exact same spot, connection to the sprinkler system will be difficult. Can the flex head work for this application? As the 1.4G is in a cabinet, I would feel better with a sprinkler head in the cabinet, with a head or heads protecting the trailer.

Any suggestions?

Douglas Hicks
General Fire Equipment Co of Eastern Oregon, Inc


Oops, I was not clear enough on the "these explosives are comparable to fireworks" I did not mean the arial rockets. I meant the kind you get from the tents for the kids to fire off for the Fourth of July. Maybe I should have said "pyrotechnics", as these are like you might see at a rock concert. But keep the comments coming. When I told the FM I would post on the Sprinkler Board, he was relieved to have the input from the Board.
_______________________________________________

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080 _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to