Most carpeting meets the definition of non-combustible, but I would
suggest checking the manufacturers cut sheet to verify.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Margaret
Zabel
Sent: Thursday, July 31, 2008 11:39 AM
To: Sprinkler Forum
Subject: Stair shafts

Using NFPA 13-2002, paragraph 8.14.3.2 describes the
requirements for sprinklers in non-combustible stair
shafts.

Would a non-combustible construction stair shaft
(concrete stairs, sheetrock/rated walls) that has
carpet on the landings and stair treads be considered
"non-combustible"?  Assuming the stairs are over 4'-0
wide, should there be sprinklers located throughout
the shaft -- below treads and stairs?

Thank you,

Margaret Zabel
Cisco Fire Sprinklers