Is this a multiple story building? If so, don't you still have to protect the landings where egress and access happen?? Regardless of combustible finishes?? NPFA 13; 8.15.3.3
-----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of John Drucker Sent: Thursday, July 31, 2008 11:06 AM To: [email protected] Subject: RE: Stair shafts Maybe. Floor coverings, specifically carpet is considered interior finish pursuant to 2006 IBC 804.4 and as such Class I (I-1 and I-2) , Class II materials (A,B,E,H,I-4,M,R-1,R-2 and S) and DOC FF-1 compliant in all the others. The exception allows interior finish requirements to be bumped down one grade where a building is equipped throughout with an an automatic sprinkler system in accordance with 2006 IBC 903.3.1.1 or 903.1.2. 903.3.1.1.1 -4. Exempts "In rooms or areas that are of non combustible construction with wholly non combustible contents". So if the interior finish materials meet the non combustible criteria then sprinklers are only required at the top and bottom levels of a non combustible stair. Someones got to go back to the carpet manufacturer for the answer. PS, Change Stair Shaft to Stair Enclosure. Hope that helps John Drucker Fire Protection Subcode Official (AHJ, not a scientist ;-)) New Jersey -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Margaret Zabel Sent: Thursday, July 31, 2008 11:39 AM To: Sprinkler Forum Subject: Stair shafts Using NFPA 13-2002, paragraph 8.14.3.2 describes the requirements for sprinklers in non-combustible stair shafts. Would a non-combustible construction stair shaft (concrete stairs, sheetrock/rated walls) that has carpet on the landings and stair treads be considered "non-combustible"? Assuming the stairs are over 4'-0 wide, should there be sprinklers located throughout the shaft -- below treads and stairs? Thank you, Margaret Zabel Cisco Fire Sprinklers _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) CONFIDENTIAL AND PROPRIETARY: This email message is intended only for the use of the individual or entity to which it is addressed and may contain information that is privileged and confidential, nor is it, unless specifically stated, intended to be relied upon by any person or persons other than the individual or entity named above and no warranties or representations are made or intended to persons or entities not named above. If the reader is not the intended recipient, you are hereby notified that any dissemination, distribution or copying of this communication is strictly prohibited. If you have received this communication in error, please notify us immediately by telephone, return this message to the address above and delete all copies. Thank you. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) No virus found in this incoming message. Checked by AVG. Version: 7.5.524 / Virus Database: 270.5.10/1584 - Release Date: 7/31/2008 12:00 PM No virus found in this outgoing message. Checked by AVG. Version: 7.5.524 / Virus Database: 270.5.10/1584 - Release Date: 7/31/2008 12:00 PM _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)