Jack,

I think most would agree that a flat curve on a source producing 1500 gpm at
a residual of 95 psi is to say the least acceptable, how far out in pressure
do we hit 4,000 - 5,000 gpm, 77psi ?. Whats the most system demand with hose
stream on a typical LH, OH1 even an OH2,  700 gpm perhaps ?  If I had your
water pressure the fire pump guys in town would be crying. 

Its unfortunate in Joes case that a code official isnt willing to look at
the big picture.

John

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Thursday, July 31, 2008 9:31 PM
To: [email protected]
Subject: RE: Water Supply

John

Sometimes not that easy: This printer was allowed to tap into an 18" 
trunkmain, as that was the only reliable main within 1 mile. 
We started the flowtest with 250 gpm, then went to 500 gpm,  750 gpm, 1000 
gpm, 1250 gpm, and hit 1500 gpm, (this was 125% of total demand for 
sprinklers and hoses) just to see a pressure drop, the pressure dropped 
from 98 psi to just 95 psi. The water utility said to drop the pressure by 
25% we need to follow hell of a lot more, we may flood some streets and he 
would not allow this full-stop.

Cheers
Jack C Kilavuz
Assistant Director
Managing Consultant - RMS
Royal & Sun Alliance Insurance - Singapore
77 Robinson Rd #17-00, Singapore 068896
DID:   (+65) 6423 0552
Fax:    (+65) 6423 0798
Mobile   (+65) 9277 5741
Website: www.rsagroup.com.sg
Note new e-mail address: [EMAIL PROTECTED]
Please consider the environment before printing this e-mail!

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to