I had been involved with a similar occupancy that was insured by FM
Global. I personally thought that their criteria was light for the
occupancy, but this is what they wanted. See if there is an HPR
company involved and get their take on it.
At 02:55 PM 8/7/2008, you wrote:
Interesting since NFPA 13 A.5.6.3 (2007) lists foam mattresses (in
finished form) as a Group A Plastic. Box springs which are mostly
wood and metal as Class III.
I would consider the foam in the sofas and probably lean toward
classifying them the same as the mattresses.
They probably looked at Furniture, with plastic coverings - Class
IV. But with foam plastic cushioning it's back to Group A plastics (sofas).
Somebody messed up. Need to remind them of Sofa World. This stuff
burns fast and hot and flows.
You need to look at the racks again too.
Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Andy Johnston
Sent: Thursday, August 07, 2008 2:29 PM
To: [email protected]
Subject: Mattress stroage
I am working on a bid for a warehouse. I was given a floor plan for
the new building and a copy of the fire plan from the same building
they just finished in another state.
The also sent photos of the existing building.
The pics show mattress in plastic bags staked on end all lined up in a row.
Just like in dramatic burn video I recently watched.
The other area of the warehouse has couches bagged the same way.
Sitting on 12'3" bay racks.
The sprinkler plans for the this are list it as Class IV commodity
protected with EFSR heads and no in rack system.
Even if they put the stuff back in the boxes I can't see how they a
class V commodity
Is there some thing I am missing before I call the engineer?
Thank you for your attention.
Andy Johnston
Andy Johnston
Master Craft Plumbing Contractors Inc. Phone (386)252-7047 Fax (386)898-0322
Your are welcome to call my Cell (386)547-4970
The information contained in this transmission is privileged and
confidential. No reader may make any use of it's contents with out
the written approval of the sender. The recipient should not act or
use the information in this transmission or any of its attachments
without separate authentication of its authenticity or approval. If
you have received this in error I apologize please notify me so I
can correct my records. Thank you for your cooperation.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)