Double check the occupancy classification. If it's still considered an
R3 (single family), then 13D should be ok. If a different occupancy
classification such as an "I" then it's no longer considered a single
family but a commercial hence a full 13 system may be required. The
local building and/or fire code should dictate if a sprinkler system and
which type of sprinkler system is required in a given occupancy.  Then
the specific standard will tell you how to install it.

Building/Fire Code= Where to install sprinklers    NFPA Standards= How
to install sprinklers.

Hope this helps.

Steve 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Russell
Sent: Friday, August 08, 2008 6:41 AM
To: [email protected]
Subject: RE: 13D buildings

I need to add that the building is used as a daycare. In my state the
entire building can be 13D and designed as one dwelling unit.