Right. And I have run into locales where a #13D is acceptable for a day
care, egress is the only concern. In the first that comes to mind, we
sprinklered portions of a church used as daycare, along with the egress
corridors, with #13D and a 2-head flow, #13D tank and pump.

There is no restriction on # of floors with a tank and pump as supply. The
para under supplies was simply an option to offer a cost savings (less water
storage) if you had a dinky house with quick egress.

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Russell
Sent: Friday, August 08, 2008 9:12 AM
To: [email protected]
Subject: RE: 13D buildings

Sorry, I mis-wrote when I wrote "This suggests to me that it can have more
floors if the system is supplied by a tank as the sole supply." I meant to
write "This suggests to me that it can have more floors if the sole supply
is NOT a tank".
Anyway, I would think that there would be some floor limits, but must not. I
missed the earlier forum discussion you referenced.

Thanks 


 

Russell Rewis
Brown Automatic Sprinklers, Inc.
107C Hemlock Street
Valdosta, Georgia 31601
229-244-8130
[EMAIL PROTECTED]

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George Church
Sent: Friday, August 08, 2008 8:49 AM
To: [email protected]
Subject: RE: 13D buildings

Re-read the supply section; you can reduce the duration from 10 to 7 minutes
if you have a single story house <2,000 SF. Nothing to do with the scope of
the standard.

I saw nothing in the scope of the standard offering evidence of a
restriction, hence the discussions on this Forum of 20,000 SF homes with
bowling alleys, parking garages, etc. 

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Russell
Sent: Friday, August 08, 2008 8:05 AM
To: AFSA
Subject: 13D buildings

I need help finding something again. Becoming a habit lately. How many
stories can a 13D building have? The only reference to this is in the water
supply section under tanks as the sole supply where it states that one of
the requirements is the building cannot be more than one story. This
suggests to me that it can have more floors if the system is supplied by a
tank as the sole supply. I'm looking at a two story building with 2400 s.f.
each level.

 

 

 

 

 

Russell Rewis

Brown Automatic Sprinklers, Inc.

107C Hemlock Street

Valdosta, Georgia 31601

229-244-8130

[EMAIL PROTECTED]

 
in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to