Ron Greenman wrote:

>You some type of fixture similar to a fire pump test header downstream
>of the backflow preventer that is of a size sufficient to flow the
>design demand.

*Tanks Ron for good input. Fire bad.

Karen,

Depending on how your riser is configured.....you may be able to install one
or more hose valves right off your riser piping. Certain parts of Maryland
are big on this, but when we configured it this way....we never had an
issue. We were fortunate enough to have outside exits where we could run our
test hoses out to our hose monsters.

This subject was another post not to long ago regarding this. You may want
to search the archives for other ideas. I think it may have even been my
post, but it was mentioned that 13 tells you have to provide for this, but
the how to go about it gets left to the imagination. I recall asking the
code official if a grooved tee with a cap would suffice. After all you could
remove and hook a test apparatus up. Right? He didn't buy it, but the two
hose valves downstream of the BFP he Ok'd. Depending on how much you got to
flow this may not work.

DOE....a deer?

Hope this helps.

Ken Holsopple
Design Manager
Rowe Sprinkler Systems, Inc.