Learned list serv members:

A consultant has shown a new double check valve backflow prevention
device to be installed in the suction side of a fire pump(s) system.
The fire pumps (horizontal split case) draw from a tank that is located
below the pump.  It has been in service for many years without a
backflow preventer and without a problem.  The requirement for a BFP is
evidently our own, though I haven't researched that as yet.

NFPA 20 says 

5.14.9* Devices in Suction Piping.
5.14.9.1  No device or assembly, unless identified in 5.14.9.2, that
will stop, restrict the starting, or restrict the discharge of a fire
pump or pump driver shall be installed in the suction piping.    
5.14.9.2  The following devices shall be permitted in the suction piping
where the following requirements are met: 
(1)     Check valves and backflow prevention devices and assemblies
shall be permitted where required by other NFPA standards or the
authority having jurisdiction.
(2)     Where the authority having jurisdiction requires positive
pressure to be maintained on the suction piping, a pressure-sensing line
for a low suction throttling valve, specifically listed for fire pump
service, shall be permitted to be connected to the suction piping.
(3)     Devices shall be permitted to be installed in the suction supply
piping or stored water supply and arranged to activate a signal if the
pump suction pressure or water level falls below a predetermined
minimum.
(4)     Suction strainers shall be permitted to be installed in the
suction piping where required by other sections of this standard.
(5)     Other devices specifically permitted or required by this
standard shall be permitted.

A.5.14.9  The term device as used in this subsection is intended to
include, but not be limited to, devices that sense suction pressure and
then restrict or stop the fire pump discharge. Due to the pressure
losses and the potential for interruption of the flow to the fire
protection systems, the use of backflow prevention devices is
discouraged in fire pump piping. Where required, however, the placement
of such a device on the discharge side of the pump is to ensure
acceptable flow characteristics to the pump suction. It is more
efficient to lose the pressure after the pump has boosted it, rather
than before the pump has boosted it. Where the backflow preventer is on
the discharge side of the pump and a jockey pump is installed, the
jockey pump discharge and sensing lines need to be located so that a
cross-connection is not created through the jockey pump.

1.  Is there a problem with locating the BFP in the suction side and
what may that be?  I don't really understand the statement "It is more
efficient to lose the pressure after the pump has boosted it, rather
than before the pump has boosted it. "

2.  Has anyone looked into this type of situation where the BFP in the
suction side of the centrifugal pump actually created a problem
regarding the net positive suction head (NPSH) required for the pump?  I
haven't done the calculation, but am curious if this is a deal breaker
for the possibility of placing the BFP in the suction when drawing water
from a tank with a centrifugal pump.  

3.  Why would a BFP be required for the fire service in the first place?
Would the fire pump test header (with hoses connected) be reason to
install a BFP on the suction side of the fire pump? 

4.  If I put the BFP on the discharge side, would the test header still
be a problem with respect to backflow?

Thanks

Pete
VA