Short answer NO! The cabinets are not "Gas Tight" and will become filled with the FM200 just at a slower rate, than the rest of the room.
Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Reza Esmaeili Sent: Wednesday, September 03, 2008 7:48 AM To: [email protected] Subject: FM-200 enclosure volume (Exclude Cabinets volume?) Hi all, To determine the enclosure volume for designing a FM-200 system in a computer room, should/ can I exclude the volume of cabinets inside the room? The cabinets are like this picture: http://www.sarian.ir/images/cabinet.jpg and the cabinets volume are about 10% of total enclosure volume. My desion concentration is 7.4%, if I don't exclude the volume of cabinets then the real design concentaration would be 10% more which is 8.14%, I know 8.14% is also acceptable, but I want to be cost effective, so can I exclude the volume of cabinets? Thanks, Reza _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)