Generally "Furniture" would not extend up to the ceiling, and so not be blocking the spray pattern, that developed for the room. A converted closet will since there is a lintel over what used to be the door that extends to the ceiling. The secondary issue is if the area was included in the area of protection provided by the sprinklers in the room, formerly the "Adjoining room"? If not some method of protection should be supplied, unless a specific exception can be met.
A single head at the top of the closet/linen cabinet should suffice. If you add 14-15 Gpm to a 3x3 space, that cooling effect will be huge, and while water may not directly contact the burning materials, the normally loose fitting shelves of a cabinet, will allow the water to wet the interior surfaces of the cabinet all the way to the floor. So unless this is a "Suppression mode" system, I would say "containment" was the likely result, if a fire occurred in the cabinet/closet with a single sprinkler head at the top. My two peso's, and well worth it, Se? Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Roland Huggins Sent: Wednesday, November 05, 2008 9:08 AM To: sprinklerforum@firesprinkler.org Subject: Re: Closets / cabinets I go with what Ron said. Also note that obstructions (shelves) are not an issue in a closet. Also it is A.8.15.8.2 that states that sprinklers are not required within furniture is the old text and it was expanded in 07 (and put within the standard ) at 8.1.1(7). That section also states you can attach the furniture to the structure. It doesn't say you can put it within a closet. Roland On Nov 5, 2008, at 7:27 AM, Ron Greenman wrote: > I tend to agree with Allen if I'm understanding his argument > correctly. And correct me if I'm misstating the thought but I don't > think he meant that the recess did not necessarily have to have > separate protection but that the floor area had to be accounted for by > some sprinkler. If I buy a free standing entertainment center I have a > potential fire hazard (lots of plugs and cords) and the area of the > building it occupies is protected by the overhead system. I am not > going to worry about a fire inside it until that fire breaches the > cabinet itself. By the same token if I have a built-in entertainment > center I have the same hazard and must consider the building area it > occupies if the fire breaches the cabinet. If that occurs then the > building must be protected (protecting the cabinet in both cases is my > concern, not society's, and could be addressed by a wonder gas if I so > desire). Now if I use a former closet for my cabinet, using a face > frame, with or without doors, and the former closet door lintel is an > obstruction, and the closet does not meet any of the closet exemption > rules then it would require a sprinkler on the closet side of the > lintel. The same issues would apply if I just put a free standing > cabinet in the closet opening. The cabinet parts are just a > distraction in this discussion. The issues are the lintel (i.e.: > obstruction) and sprinkler spacing rules. _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)