1% (That would be 5 if you had 500 of all the same type and temp.) If say you had 200 SSU and 200 SSP and 100 HSW, then you would need to supply 4 of each type.)
Remember, if even one fails, you replace all the sprinkler in the area that sample represents. NFPA 25, 2008 5.3.1.3. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Dyce Geoffrey H. Sent: Monday, November 17, 2008 3:37 PM To: [email protected] Subject: Testing Sprinklers We have a situation where there are aprox. 10 warehouse systems with sprinklers over 50 years old which include offices, racks, and ceiling sprinklers. If each system has 500 +/- sprinklers and each sample requires 4 sprinklers or 1%, whichever is greater, what would you call a representative sample of this building? Thanks in advance Geoffrey H. Dyce Sales Manager Contractor I, #87582700012007 NICET IV Industrial Fire & Safety Inc. Ph: 727-573-1556 Fx: 727-572-7266 Cell: 727-644-8872 _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)