The Annex material further elaborates that it does not have to be every single type of sprinkler with SIMILAR sidewall, pendent, and upright sprinklers by the SAME manufacturer being in the same representative sample.

Roland

On Nov 17, 2008, at 2:36 PM, Dyce Geoffrey H. wrote:

We have a situation where there are aprox. 10 warehouse systems with sprinklers over 50 years old which include offices, racks, and ceiling sprinklers. If each system has 500 +/- sprinklers and each sample requires 4 sprinklers or 1%, whichever is greater, what would you call a representative sample of this building?
Thanks in advance