Ron,
Read it closer.  The NEC allows sprinkler "protection" where the pipe
conforms to the dedicated space requirement.  In other words, sprinkler
protection is allowed as long as the pipe itself is not installed above the
electrical panels.

(Embedded image moved to file: pic17864.jpg)


Thank You

Rahe Loftin, P.E.
Region 7 - GSA
Office - 817-978-7299
Fax - 817-978-8644
Cell - 817-371-3102



                                                                           
                                                                           
             "Fletcher, Ron"                                               
             <rfletc...@aerofi                                          To 
             re.com>                   [email protected]    
             Sent by:                                                   cc 
             sprinklerforum-bo                                             
             un...@firesprinkl                                     Subject 
             er.org                    RE: Electrical Rooms                
                                                                           
                                                                           
             12/16/2008 10:03                                              
             AM                                                            
                                                                           
                                                                           
             Please respond to                                             
             sprinklerfo...@fi                                             
              resprinkler.org                                              
                                                                           
                                                                           




There is an exception for sprinkler pipe.

Exception:  Suspended ceilings with removable panels shall be permitted
within the 1.8-m (6-ft) zone.

(b)      Foreign Systems. The area above the dedicated space required by
110.26(F)(1)(a) shall be permitted to contain foreign systems, provided
protection is installed to avoid damage to the electrical equipment from
condensation, leaks, or breaks in such foreign systems.

(c)      Sprinkler Protection. Sprinkler protection shall be permitted
for the dedicated space where the piping complies with this section.

(d)      Suspended Ceilings. A dropped, suspended, or similar ceiling
that does not add strength to the building structure shall not be
considered a structural ceiling.


Ron Fletcher
Aero Automatic Sprinkler
21605 N. Central Ave
Phoenix, AZ 85024
P: 623.580.7836
F: 623.434.3420
C: 602.763.4160
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Tuesday, December 16, 2008 8:47 AM
To: [email protected]
Subject: Re: Electrical Rooms

NEC Article 110.26(F)(1)(a).

Dedicated Electrical Space. The space equal to the width and depth of
the
equipment and extending from the floor to a height of 1.8 m (6 ft) above
the equipment or to the structural ceiling, whichever is lower, shall be
dedicated to the electrical installation. No piping, ducts, leak
protection
apparatus, or other equipment foreign to the electrical installation
shall
be located in this zone.

Thank You

Rahe Loftin, P.E.
Region 7 - GSA
Office - 817-978-7299
Fax - 817-978-8644
Cell - 817-371-3102







             "Brian Harris"

             <br...@firstdefen
To
             sefire.com>               [email protected]

             Sent by:
cc
             sprinklerforum-bo

             un...@firesprinkl
Subject
             er.org                    Electrical Rooms





             12/16/2008 09:36

             AM





             Please respond to

             sprinklerfo...@fi

              resprinkler.org









I know it's in the code but I can't put my finger on it, what section
talks
about not running a sprinkler line through an electrical room? While I'm
on
it what section prohibits running through a stairwell? Thanks, I'm in a
time
crunch otherwise I wouldn't bother you........


Regards,


<http://www.firstdefensefire.com/>








E-mail message checked by Spyware Doctor (6.0.0.386)
Database version: 5.11350
http://www.pctools.com/en/spyware-doctor-antivirus/
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to