I once found a drawing done by a counterpart who drew sprinkler lines, located 
heads, sized the pipe, located the hydraulic remote area and drew hydraulic 
nodes on the drawing.  When I asked some questions like how did you come up 
with the 3.5" and 5" pipe sizes he asked why, those were standard sizes used in 
mechanical process design, so what was wrong?  Then I asked about the hydraulic 
nodes and remote area and where the calcs were, (I knew what was coming) he 
said they didn't do any calcs.  I pointed out that it would be pretty hard to 
successfully size pipe on a gridded system & determine the exact remote area 
without running calcs since he had very little if no design experience.  I also 
mentioned that since it was a dry system he couldn't grid it.  He also didn't 
have any water data, again I pointed out how that could cause a problem with 
doing calcs.  I got a somewhat defensive response.  Fortunately the document 
was never actually released.  

I've been corrected by MPE's (some of them actually own their own copy of NFPA 
13) on how a sprinkler shop drawing should look.  I have challenged their 
position based on the fact that I HAVE produced innumerable shop drawings as a 
contractor and they have produced ZERO.  Yet since they are the PE they 
obviously must be right.

Had a fire chief who was acting as the AHJ for the county tell a client they 
didn't need to sprinkler their electrical room be cause he didn't like it.  
Unfortunately for the client, their specific condition was going to require 
sprinklers in these rooms and there was no way to get around it.  This same guy 
gave them directions to disable other systems because he didn't' feel they were 
necessary.  

And I'm sure we could all go on and on and on.

Yes, the level of ignorance is huge.  All you can do is educate every time the 
opportunity arises and hope for the best.




Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of George Church
Sent: Thursday, January 08, 2009 7:59 AM
To: [email protected]
Subject: RE: The Engineering Problem (RE: another fire -thiswillbeinteresting)

Be serious. 

I love calling an engineer and asking if they know the water supply. When they 
say No, I ask where the fire pump goes and if its elec or diesel.
When they ask why a pump is needed, I ask how do you know if we need a tank or 
pump or not if you don't know the water supply?

Reality is that no matter what the White Paper says, we deal with ignorance 
daily. The bigger question is, who checks the checker- especially when you know 
the ignorant PE is as bad as the ignorant inspector (ignorance meaning lack of 
detailed knowledge needed, nothing further. I'm ignorant of a lot of things 
myself).

Guess it's a good thing there are tons of safety margins built into all the 
codes so a crappy job still works just fine, no one will die.....

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Tom Duross
Sent: Thursday, January 08, 2009 7:46 AM
To: [email protected]
Subject: RE: The Engineering Problem (RE: another fire -
thiswillbeinteresting)

Did anyone notice a surge in MEP firms performing hydraulics in the past few 
years?

Tom

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to