George,

If you are operating out of the IFC, Section 903.3.7 tells you the location
shall be approved by the fire code official.  In most jurisdictions that we
work in the fdc is to be within 75 feet of a hydrant.  

Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com


-----Original Message-----
From: George Medina Jr [mailto:fireg...@aol.com] 
Sent: Thursday, January 08, 2009 10:14 AM
To: sprinklerforum@firesprinkler.org
Subject: FDC TO HYDRANT DISTANCE

Can somebody refer me to the code section that specifies the distance from
the FDC to fire hydrant?


George Medina Jr.