Russel,

The problem is that you cannot directly connect a pressurized water
system to a gravity system. Nor can you have a direct connection
between a potable water system and a waste system. Even though the
backflow device protects the potable water from the horrible sprinkler
water it doesn't protect it from sewage and if you make a direct
connection a waste line you've just directly connected your municipal
water supply to your municipal sewage treatment plant. And to the
dirtier end. What you want is a receiver of some sort with a proper
air gap. The receiver has to accommodate the overflow from the
pressurized system while it's running without overflowing. Think of a
sink as a receiver between the pressurized piping of the water system
and the gravity piping of the waste piping. The air gap between the
faucet outlet and the flood rim of sink is to prevent backflow. The
proper distance for an air gap is 2 and 1/2 times the diameter of the
discharge orifice.


On Fri, Jan 9, 2009 at 6:56 AM, Russell <russ...@brownautomatic.com> wrote:
> I have a situation where the inspector's test discharge cannot be piped to
> the outside or a floor drain. I do have though, a domestic waste pipe near
> by. I know that NFPA13 does not allow direct connection of the two and I
> think I understand the reason for this, but can a check valve be put in the
> test discharge pipe to satisfy the NFPA requirement? Does anyone know of
> some sort of air gap device or other method to accomplish this? Never faced
> this situation before. Any suggestions will be greatly appreciated.
>
>
>
>
>
>
>
> Russell Rewis
>
> Brown Automatic Sprinklers, Inc.
>
> 107C Hemlock Street
>
> Valdosta, Georgia 31601
>
> 229-244-8130
>
> russ...@brownautomatic.com
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: techsupp...@firesprinkler.org
>
> To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Reply via email to