That's just one way; and you can drain to sanitary sewer per the
plumbing code, but you have to use an approved receptor.  Which may
include a hub drain, a floor sink or a floor drain.  All of these
require a trap, which itself is required to be a self-priming trap if
it's 3" or larger, which is what we generally specify.   You don't need
a backflow appliance, but there is an air gap.   The only difference
between a hub drain and the other two is that it's above grade, which
makes it ideally suited to exterior applications.  But expense isn't a
big issue - these are all off-the-shelf parts in the plumbing world, and
if you are prohibited (as we are in much of California now) from
discharging to storm, these are simple solutions. 

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Friday, January 09, 2009 7:33 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Sprinkler system interconnection to domestic waste pipe

You need what is called a hub drain.  Then route the I.T. to it, leave
the appropriate air gap and you're done. 

Unfortunately the hub drain also requires other plumbing for keeping the
trap primed and the expense of installing one might not be justified for
your sprinkler drain.




Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
craig.pr...@ch2m.com
http://www.ch2m.com 


-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Russell
Sent: Friday, January 09, 2009 9:57 AM
To: AFSA
Subject: Sprinkler system interconnection to domestic waste pipe

I have a situation where the inspector's test discharge cannot be piped
to the outside or a floor drain. I do have though, a domestic waste pipe
near by. I know that NFPA13 does not allow direct connection of the two
and I think I understand the reason for this, but can a check valve be
put in the test discharge pipe to satisfy the NFPA requirement? Does
anyone know of some sort of air gap device or other method to accomplish
this? Never faced this situation before. Any suggestions will be greatly
appreciated.

 

 

 

Russell Rewis

Brown Automatic Sprinklers, Inc.

107C Hemlock Street

Valdosta, Georgia 31601

229-244-8130

russ...@brownautomatic.com

 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 3754 (20090109) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 3754 (20090109) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Reply via email to