Jimmy,

Three thoughts.

First, how's he ignoring the requirement that the minimum 1.2 x sqrt of MRA must be parallel to the branch lines?

Second, how's he ignoring 22.4.4.1.1.3, which allows for such cases?

Third, make him do two calculations, one his way, one the way we're describing it to you, and see which one is most demanding. All things being equal, his way won't be.

Then ask him to guarantee in writing, and back it up with a bond, that there won't ever be a fire in which grows to achieve the worst case flow, and see what he says.

And hey, maybe he's right and the rest of us have been wrong all these years. We can always learn something.