I am a freelance designer and I never understood this arguing with a
customer.  Running a calc should take no more than a few minutes.  In
AutoSprink it takes about 10-20 seconds to draw a remote area depending on
how complex and cut up it is.  He should be able to quickly check and see
what area is most demanding.  It seems like a no brainer.

I think George has the right idea.  A freelancer should not do anything that
he knows is in conflict with NFPA, but should be willing to do what the
customer asks as long as there is no conflict.

Just tell the guy to run the second calc and stop complaining.  If he is
right, he proves his worth to you and you will likely use him for all jobs
in the future.  If he is wrong, but handles himself professionally, you will
likely use him on more jobs in the future.  If he is wrong and handles
himself like an @$$, you will never use him again.  The ball is in his
court.

Good luck with it.  Let us know how it comes out.

That is the beauty of this forum, it lets us learn from others experiences.
Now, for my plea for all freelance designers out there: If you use this
email forum and learn from it, pay the $200 AFSA designer dues and support
the forum.  I know I have well earned back my yearly dues with all of the
knowledge gained from this forum.  Too bad it does not count for NICET
credits.  I learn more here than some of the seminars I have taken for CPD
credits. 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Wednesday, January 21, 2009 7:43 AM
To: [email protected]
Subject: RE: 1.2 Leg of Remote Area

Well, I guess the other way to convince him would be to tell him  you'll pay
him to do it the way YOU think is right, and if he elects to calc it another
way for free, hey- it's a free country. And he needs to understand the
pecking order- you've got the checkbook.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Joe Burtell
Sent: Wednesday, January 21, 2009 8:42 AM
To: [email protected]
Subject: RE: 1.2 Leg of Remote Area

First: He is stating that because the longer leg in now parallel to the
crossmain, the code says you must still meet the 1.2 times rule on the
longer leg.
Second: Because he feels he must satisfy the 1.2 rule.

Joe
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Tuesday, January 20, 2009 5:18 PM
To: [email protected]
Subject: Re: 1.2 Leg of Remote Area

Jimmy,

Three thoughts.

First, how's he ignoring the requirement that the minimum 1.2 x sqrt of MRA
must be parallel to the branch lines?

Second, how's he ignoring 22.4.4.1.1.3, which allows for such cases?

Third, make him do two calculations, one his way, one the way we're
describing it to you, and see which one is most demanding.  All things being
equal, his way won't be.

Then ask him to guarantee in writing, and back it up with a bond, that there
won't ever be a fire in which grows to achieve the worst case flow, and see
what he says.

And hey, maybe he's right and the rest of us have been wrong all these
years.  We can always learn something.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[email protected] <mailto:[email protected]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

__________ NOD32 3785 (20090121) Information __________

This message was checked by NOD32 antivirus system.
http://www.eset.com


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to